Discuss CH pump replacement concerns. in the Central Heating Forum area at PlumbersForums.net

6m pump John. I'm running it at Proportional 3. 34W 4.2m head 3.3cu m per hour initially. Will monitor it more closely after I've rebalanced the rads. 13 of the rads have thermostatc valves so I expect to see differences as house warms up.
 
I interpret from the pump curves that the flowrate is 1.02m3/hr, 17.0LPM which, depending on the rads output may give a dT of 15C to 20C.
 
1711222010885.png
 
Apologies John. Typo on my part. Indicated flow rate is indeed 1.3 cu m per hour and your delta T of between 15 to 20 deg C across the boiler is spot on. Delta T across radiators is very variable because of thermostatic valves. Delta T across boiler drops when hot water cylinder calls.
 

Reply to CH pump replacement concerns. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Central Heating Pump - G Pump Force HE-RS25/6PWM-130 Hi, I would be grateful if someone could explain whether our CH system can cope with the...
Replies
7
Views
605
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
669
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open...
Replies
9
Views
1K
Morning and Happy New Year everyone! As is typical over the Christmas period my Central heating circulating pump died on new years eve. It had...
Replies
7
Views
2K
Been renovating my house and in the process improved insulation and removed quite a few rads. I've also installed more than half downstairs floor...
Replies
3
Views
749

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock