Hobo128

Gas Engineer
Messages
302
Went to a job the other day, customers boiler had stopped working. i took the casing (combustion casing off) and it lit up. I put the case back on and it stayed lit. When I turned it off and back on it didn't light Dhw or Central heating. I checked the air pressure that was fine and checked the flue for blockages and all was fine.

Boiler is Sime Ecofort plus 30 HE

Any idea's.
 
It's an air supply problem, usually aps or a blockage around it. Ie on the hose or the Venturi on the flue. Split aps hose etc etc.
 
Zeb bang on defo an air supply issue. As itd gettin plenty air with casing off. Like already said check flue, hoses, venturi. + air pressure sw.
 
As has been said, air supply. Check flue, APS and hoses, fan venturi etc.
 
Check your training . Sime - any fault died with axe. It's air supply as evacuation would cause excessive heat and o/h lock down. Check Venturi tubes in the flue not all pooped
 
Status
Not open for further replies.

Reply to Boiler only fires with casing off! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
341
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
225
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock