mke4442
I have an annoying fault which has crept in recently. My boiler started to trip out on overheat, despite the boiler thermostat being set at 50% full scale. BG have visited 5 times and have
1. Replaced motor on the pump as it had overheated. See second visit....
2. Opened the pump spill back valve a little. This was causing the pump to overheat.
3. Changed the boiler thermostat (not the overheat thermostat)
4. Changed the PCB
The trips are less frequent now but for 4 weeks the boiler has been cycling on and off on a 45 second cycle, so the water never gets hot enough. Not good for the boiler either.
I asked BG to visit once again and their specialist arrived.
5. He crawled into the roof space to check the 22mm hot and cold manifolds that run around the house with a magnet. (Note we have 15mm drop pipes to feed the radiators in each room). They advised that they had found a partially blocked 22mm pipe, I don't know where or if hot or cold) which they offered to cut out and replace. They also recommended a system power flush.
Well, I took the power flush option first as costs are high with BG. Needless to say there has been no improvement in cycle time so I am lost as to the next step.
Any suggestions please??
1. Replaced motor on the pump as it had overheated. See second visit....
2. Opened the pump spill back valve a little. This was causing the pump to overheat.
3. Changed the boiler thermostat (not the overheat thermostat)
4. Changed the PCB
The trips are less frequent now but for 4 weeks the boiler has been cycling on and off on a 45 second cycle, so the water never gets hot enough. Not good for the boiler either.
I asked BG to visit once again and their specialist arrived.
5. He crawled into the roof space to check the 22mm hot and cold manifolds that run around the house with a magnet. (Note we have 15mm drop pipes to feed the radiators in each room). They advised that they had found a partially blocked 22mm pipe, I don't know where or if hot or cold) which they offered to cut out and replace. They also recommended a system power flush.
Well, I took the power flush option first as costs are high with BG. Needless to say there has been no improvement in cycle time so I am lost as to the next step.
Any suggestions please??