I have a holiday cottage in a remote location without mains gas. The lpg hot water / central heating system has a recently installed high efficiency condensing boiler. I don't have space for a large lpg tank so use the 47kg bottles and these are expensive. The cottage is getting through a great deal of pg and gaining access to the property in severe weather is difficult so lpg deliveries aren't guaranteed. As the cottage is let I don't really want paying guests freezing..
The cottage will be well insulated (still needs to be finished) and has double glazing throughout. Unfortunately it has wooden floorboards but these are covered throughout with the aim of minimising drafts. Cavity wall insulation still to be installed but this is planned.
I am looking to possibly install an ASHP as the main source of energy for hot water and central heating. I know I need to oversize the radiators, these need replacing anyway.

I am thinking of using installing an ASHP in such a way as to allow switching between ASHP and lpg boiler. ASHP used mainly, but for the lpg boiler to provide a manual boost (possibly via the Internet as I live 300 miles away) in extreme weather conditions when it is least efficient and when the lower radiator temperature isn't sufficient to heat the house. I don't like to heat the cottage unnecessarily so to keep it ticking along when it isn't let is probably ideal via an ASHP with the thermostat set low.

I am thinking of installing a Daikin Altherma monobloc LT ASHP. One of the new 8kW units should be adequate, although I will seek advice on this - 3 bed semi-detached bungalow. BTW - not enough space for a GSHP and not really enough space for an indoor unit to accompany the ASHP.

I'm not a plumber, but enthusiastic amateur!

Do you know if this approach has been done before?
Do you see any problems with it?

I have a general question about ASHPs. I understand that the COP changes with temperature. If an ASHP is rated at 8kW will it always give 8kW over the temperature range -10 to +25C and just demand more input power, or does the input power remain the same but the output drops?

Another general query - can radiators be fan assisted rather than oversizing them?
 
I have a holiday cottage in a remote location without mains gas. The lpg hot water / central heating system has a recently installed high efficiency condensing boiler. I don't have space for a large lpg tank so use the 47kg bottles and these are expensive. The cottage is getting through a great deal of pg and gaining access to the property in severe weather is difficult so lpg deliveries aren't guaranteed. As the cottage is let I don't really want paying guests freezing..

Good idea and an Ashp will be alot cheaper to run than bottled LPG

The cottage will be well insulated (still needs to be finished) and has double glazing throughout. Unfortunately it has wooden floorboards but these are covered throughout with the aim of minimising drafts. Cavity wall insulation still to be installed but this is planned.
As much insulation as possible

I am looking to possibly install an ASHP as the main source of energy for hot water and central heating. I know I need to oversize the radiators, these need replacing anyway.

I am thinking of using installing an ASHP in such a way as to allow switching between ASHP and lpg boiler. ASHP used mainly, but for the lpg boiler to provide a manual boost (possibly via the Internet as I live 300 miles away) in extreme weather conditions when it is least efficient and when the lower radiator temperature isn't sufficient to heat the house. I don't like to heat the cottage unnecessarily so to keep it ticking along when it isn't let is probably ideal via an ASHP with the thermostat set low.

Controled by room stat and out side temp sensor (weather comp)

I am thinking of installing a Daikin Altherma monobloc LT ASHP. One of the new 8kW units should be adequate, although I will seek advice on this - 3 bed semi-detached bungalow. BTW - not enough space for a GSHP and not really enough space for an indoor unit to accompany the ASHP.

Other good makes on the market and not so expensive

I'm not a plumber, but enthusiastic amateur!

Not a job realy for an amature but you could help a proffesional to keep the cost down

Do you know if this approach has been done before? Yes
Do you see any problems with it? Not with a good ASHP company with good technical back up

I have a general question about ASHPs. I understand that the COP changes with temperature. If an ASHP is rated at 8kW will it always give 8kW over the temperature range -10 to +25C and just demand more input power, or does the input power remain the same but the output drops?

All ASHP performance drop the lower the outside temperature

Another general query - can radiators be fan assisted rather than oversizing them? Yes Fan coil rads are a good option with heat pumps


I will PM you with the contact details of a very helpful ASHP manufaturerer

Eco
 
i have an eco dan 8.5kw running my house and if you get the rads sized correctly you shouldnt need anyback up really, ive had mine in since sept 2009 and been through 2 bad winters and its been minus 15 where i live. you do really want an mcs accredited fitter to do the work and then you will be eligible for the (rhi) renewable heat incentive which meens you should make money out of the heating, drop me a line if you want any help 01457 858081
 
Daikin ASHP are by far and away the best on the market. They have a new ASHP on the market that takes the temperature up to 80deg. no need to change rads or worry about not coping in extreme cold. Be aware that all ASHP outputs are quoted with an outside temperature of 7deg. so lower outside temperature lower output.
 
Thanks for the responses. Is anyone able to respond to this particular question?

If an ASHP is rated at 8kW will it always give 8kW over the temperature range -10 to +25C and just demand more input power, or does the input power remain the same but the output drops?

I suspect it just demands more input power..
 
Thanks for the responses. Is anyone able to respond to this particular question?

If an ASHP is rated at 8kW will it always give 8kW over the temperature range -10 to +25C and just demand more input power, or does the input power remain the same but the output drops?

I suspect it just demands more input power..


A 8kw ashp at 7c may only give 4kw at -7 ....... lower the temp the lower the output ......... it does depend on the make....... also watch out some makes have built in back up immersion heater and are very expensive to run ÂŁÂŁÂŁÂŁÂŁ
 
Ecowarm is quite right some do have back up heaters but you can schedule them to stay on for however long you want. They are used to pre-heat the water to about 16deg before the heat pump kicks in.
 
Status
Not open for further replies.

Reply to ASHP and LPG in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
264
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock