Discuss Adding a second Expansion Vessel? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
76
I was at a job looking at an unrelated issue when the lady mentioned her blow off keeps running outside. Apparently the last plumber replaced expansion vessel(and checked the precharge was 3bar) on the cold feed into the cylinder, 3bar pressure reducing valve and 6bar blow off in the hope to cure it.

The cylinder temp/pressure relief valve, htg relief valve and hw relief valve are all connected into one 22mm pipe. The cylinder valve has a tundish which isn't showing any signs of water, the htg pressure stays well below 3 bar and when disconnected shows no sign of letting by.

So it's all pointing to the kit on the mains pipe feeding the cylinder. I didn't take note but I want to say the vessel is around 24l and is positioned about 4 metres from the cylinder. Is it a case that an extra vessel may be needed as it's over pressurising?
 
The vessel supplied with unvented cylinder (or identical replacement) will be correct size for the unit and nothing else needs added.
Something else is faulty and it could also be elsewhere in the cold and hot water system in the house.
As said, don’t touch anything unless you have the unvented qualification or you could get the blame
 
At which point did I say I don't have the G3 qual? I do have the qualification and understand exactly how all the parts work. I have just never encountered this problem before so asked for advice, which I'm never too proud to do. Don't be so quick to judge chaps!

I think you may have nailed it Best, turns out the issues started after they had a new bathroom fitted so my guess now is no check valves on the feed to the new shower.
 
At which point did I say I don't have the G3 qual? I do have the qualification and understand exactly how all the parts work. I have just never encountered this problem before so asked for advice, which I'm never too proud to do. Don't be so quick to judge chaps!

I think you may have nailed it Best, turns out the issues started after they had a new bathroom fitted so my guess now is no check valves on the feed to the new shower.

Maybe no balanced cold then?
 
Like Best and you say Duker I’d be suspicious of something downstream back pressurising. When I used to do site work the guys used to put one PRV under sink on incoming and then obviously the one in cylinder cupboard with balanced draw off. Some people even install pressure gauges so you can see exactly what’s going on
 
A vessel installed 4M away from the cylinder is very unlikely to be the right side of a check valve if it is on the cold feed.
Could it be there for another reason other than expansion ?
I diagram would be useful as I am struggling to understand what is going on from your description Duker996.
 

Reply to Adding a second Expansion Vessel? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
517
Hi All, We have finally decided after a bit of a persuasion to have installed a utility room in our garage that currently houses our oil boiler...
Replies
7
Views
886
P
Hi. I have a hot water high pressure problem that my heating engineer (and other engineers that he has spoken to) cannot fix. I’m hoping someone...
Replies
4
Views
1K
I have recently moved into a house with the following heating system: Traditional boiler (Worcester Greenstar Ri 24 with only one temperature...
Replies
11
Views
2K
Hello forum members thanks for the welcome. This is my first post. I have a Gloworm 15hxi. Its been a really good reliable boiler. I am doing...
Replies
2
Views
515
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock