Discuss 3 radiators on 15mm branch? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
9
I was wondering whether it would be a good idea to replace some 15mm pipe with 22mm. I currently have 3 radiators on a single 15mm branch. Small, medium and large, approx 10,000BTU's at 50C in total. The room with the large radiator is always cold in the Winter, partly due to insulation but obviously a bit more heat output would help. If I were to put each radiator on its own branch, would there be any significant benefit?

I have smart heating (Evohome) so on a cold day the rads will typically be on low (or off) during the day and then high shortly before I arrive home. It would be good to minimise the time it takes to heat up as the rooms aren't always fully warm when I get home, particularly in the room with the large rad.

From what I've read, I think my setup is probably a bit borderline and not ideal. Going to 22mm would probably slightly reduce the load on the pump and have the rooms warm up a bit quicker. I'm in a position where the flooring is up and the job would be quite straight forward. I can do the work myself so the cost is minimal.

What do you think, does it sound like it would be beneficial or not? Do you always like to have each rad on their own branch when possible? Would you make the change if it was your own house?
 
10,000BTU is approximately 3kW, which is well within the capacity of 15mm pipe. Don't forget that it is only the first section which has to carry the full 3kW.

The attached file will explain why.
 

Attachments

  • Small-bore-heating-systems.pdf
    64.7 KB · Views: 1,463
You've not actually mentioned whether the rads get hot or not? If they aren't getting hot then upsize them. If they're getting hot but the room isn't getting warm then you need to look at rad sizes/insulating the room more.

Also in your Evohome Zones, have you got the HR92s for each rad on one zone for that room, and if so have you selected 'Multi Zone' in the zone settings. As otherwise it'll only be using one HR92 as the temp sensor for that zone.
 
I'm a bit confused/unsure as I've had conflicting advice in this thread. However, the replies from plumbers seem to think it's a good idea, so I'm going to give it a go.

The rads are all in different rooms/zones and they do get hot. The pump runs really well but reducing the load and noise would be even better.
 

Reply to 3 radiators on 15mm branch? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a slightly undersized radiator in my living room. The calculation says 6315 btus and my rad is 6019 btus. It was a replacement radiator...
Replies
1
Views
343
I am trying to workout in what order my radiators heat up in order to then balance them. I am able to figure out which radiator pipe is the...
Replies
1
Views
351
Hi all. I noticed this winter my living room rad only get hot in the top half. Radiator is 1600mm(DP SC) double panel single convector. System...
Replies
1
Views
458
Hi, Sorry if question already answered in previous posts, but I can't find a solution to the below: We recently moved house to a new home that...
Replies
7
Views
532
I have recently bought my own house and decided to redo the kitchen. There was a radiator in the room already but I wanted to move it. I extended...
Replies
8
Views
715
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock