ok so once I have turned half the working rads off, then what do I do? Should I turn off half the rads in the house off or just downstairs?
 
how do I check for a blockage or air lock??

Are you using a plumber or DIY ? you will need to disconnect one side off one of the new rads both ends closed, open up a valve let water into a bucket if that side is getting hot then repeat with other side , any plumber would know how to do these basic checks, total waste of time changing pipe to 22mm if its connecting back to 15mm, it should 22mm going onto 15mm, it seems your going to finish up digging up floors until you find the original 22 mm pipe.
 
it is a plumber we are using. I presume he has checked for a blockage or airlock already, but I can double check with him.

I think he is thinking that if he makes it 22mm from the boiler to the lounge it will be ok, as currently its 15mm and then to 22mm.

sounds like I could do with another plumber to come and take a look.

cheers

Ben
 
ok so once I have turned half the working rads off, then what do I do? Should I turn off half the rads in the house off or just downstairs?

turn the upstairs rads off via there trv does that one rad heat up?
 
By turning the working rads off upstairs we/you can establish whether the lounge rads are capable of working correctly or if there is a blockage or air in the system. I'd also be wary of the fact that it looks like the pipes aren't being insulated properly before being buried, we certainly can use fabric tape to protect pipes on short runs but it looks like he's taken the easiest route by digging a fairly shallow trench and wont be insulating the pipes. That's heat energy being lost to the concrete instead of your radiators.
 
Try and post a picture or drawing of the pipes from the boiler as im confused
Whats been upsized
What is planned to be upsized

Sounds like crossed wires and bad communication to me
 
Try and post a picture or drawing of the pipes from the boiler as im confused
Whats been upsized
What is planned to be upsized

Sounds like crossed wires and bad communication to me

From what I can gather he has just upsized the pipes around that room joining back on to excising 15mm but the heat load of his new rads should be ok for 15mm pipe now they are digging up rest of floor until they find 22mm
 
If he has essentially inserted a 22m section into each of flow and return, with the remainder of that flow and return in 15mm, and in particular the section between new and boiler in 15mm, then the inserted 22mm section is a waste of time. The heat carrying capacity of the entire circuit will be limited by what the 15mm can carry.

The solution of taking the 22mm pipework back to the boiler from the inserted section is the best technical solution, but sounds very disruptive. I'd want to test it by using a temporary surface laid connection in 22mm plastic before digging up floors.

It was mentioned earlier that some designer radiators MUST be connected the right way round. If they are of this type and not correctly connected, they will never heat up properly.

In terms of an action plan:

1. Check and re-check that the new radiators are connected properly.
2. Bridge flow and return from the boiler to the flow and return of the new 22mm section using surface laid plastic pipework.
3. If it still doesn't work after 2., there is something else wrong.
4. If it does work after 2. you'll have to decide whether its worth the upheaval to extend the 22mm back to the boiler or even consider putting the old radiators (or equivalents) back.
 
the plumber has upsized the pipes in one room to 22mm joining back to 15mm. now they want to dig up the rest of the floor so they can change all this piping leading to the boiler to 22mm also. I don't think they are looking for 22mm in the floor, they are just replacing the 15mm to 22mm.
 
when the plumber left he had the new rads working but with a low heat output hence him wanting to change the pipes leading to the boiler to 22mm
 
I don't think it's fair to say that connecting 22 onto the existing 15 is a total waste of time. The pressure drop is related to the length of pipe in the circuit, and a short section of pipe that is too narrow could well allow satisfactory flow even though it isn't an ideal solution (and perhaps the 15 will run noisily and the pipe walls will erode over a number of years).
Without knowing the details of how the new 22 connects to the existing 15 and how the existing 15 is run, it is hard to pass judgement, but if you are turning off other radiators (at the thermostatic radiator valves) and firing up the system and your new radiators are not getting hot at all, then the problem is something more fundemental than pipe sizing. Sounds like a total blockage (perhaps an airlock) somewhere.
 
I know that this may be a shot in the dark BUT has anyone checked that the boiler is working correctly ? and that the pump is ok ? how old is the boiler ?
 
So when I turn off the rads upstairs you can get heat going to the new rads, so does this mean that the piping size is the issue as suggested by the plumber??
 
All the new rads heat up ?

I would say it's a balancing or pump issue
 
could it be possible that the new rads are too big for the system...ie btu output? I was just thinking the system worked fine before on standard rads
 
could it be possible that the new rads are too big for the system...ie btu output? I was just thinking the system worked fine before on standard rads

Noo won't be too big and they look about right tbh
 
I would say as all the pipework is in screed its all 15mm as you have probably guessed. new combi fitted onto existing pipework? you say you turn off rads upstairs and new rads heat up....is there any pipework visible in airing cupboard or anywhere...could be an old gatevalve open acting as a bypass!! could just need balancing,doesnt sound like an airlock. pressure on boiler good?
 
that isolation valve on the return to the boiler before the filter fully open?? test the boiler on chimney sweep.
 
Ok guys so correct me if I’m wrong but firstly just connecting 22mm pipework to already 15mm pipework will do nothing to improve the heating up of those new rads. And secondly surely if the proposal of a new 22mm flow and return straight from the boiler to the new radiators would cause some tricky balancing of the rest of the house. ?? As Scott said it would be better for those rads to have been piped in 15mm straight off the 22mm flow and returns.
 
Those rads were originally piped from 15mm branched from 22mm until they were changed. Like to know if turning off the other rads worked, turn the CH on max and are you sure the hive system is set up correctly?
 
Status
Not open for further replies.

Reply to Issues with 22mm piping?? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it 😬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
263
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...