does anyone know the rate for the vaillant combi eco tec plus 837 with my calculations it being a 28kw i make the m3/hr 2.6 mi's say 4.0:confused: or am i reading it wrong.
 
MIs state 4m3 per hour, check you have the boiler set on max rate, or check your sums!!!!!!!
 
easy,on full rate just time the meter,2 mins usage x 30 = m3 per hour
 
or do the sum again and check with a gas rate slide rule,this will give you a guide and as oldplumber advised max rate when doing gas rates, i will hazard 2 guesses either you have ccn 1 core on the way and your practising or your looking at a fault
 
I only use the m3/hr for pipe sizing. Use KW (gross or net) for gas rating. As said above be sure you have boiler in max setting.
 
i was looking at pipe sizing and divided the 28kw by the cv 10.77 gave me 2.6
 
So what exactly are you trying to do? Are you trying to work out pipe sizing or are you gas rating an existing appliance?
 
does anyone know the rate for the vaillant combi eco tec plus 837 with my calculations it being a 28kw i make the m3/hr 2.6 mi's say 4.0:confused: or am i reading it wrong.

dont forget the ch output is 28kw and the hw output is 37kw, take a look at your tech data more carfully:confused: the big clue being model number of 837
 
Last edited by a moderator:
Just had a look at the 837 data and Vailant dont give the inputs just the outputs and and the gas rate of:

Connected load (if needed, related to stored charge/
water heating) at 15 °C and 1013 =mbarG20: 4.0

Coley
 
gas rate,2 min, hot water tap on full you need to get corgi gas rate slide chart,£9,
fga test
 
@old plumber

Well spotted we have just installed a ecotec too I forgot the data required was futher down.

Thanks
Coley
 
Hi

If you log on to [DLMURL="http://www.vaillantdownloadservice.co.uk"]Vaillant Technical Download Service[/DLMURL] you can download all technical information on all Vaillant products.
 
Last edited by a moderator:
"vaillant technical" is a contradiction in terms !!
vaillant librarians is a better descriription, but your on the right lines using their web service - if the page loads in less than 45 minutes your still be better off than ringing them !


if only they'd listen to people and sort their tech help side of things sorted out, they might have a chance at the future market.
 
"vaillant technical" is a contradiction in terms !!
vaillant librarians is a better descriription, but your on the right lines using their web service - if the page loads in less than 45 minutes your still be better off than ringing them !


if only they'd listen to people and sort their tech help side of things sorted out, they might have a chance at the future market.
migo are you on the vino already?simple calc,gas rate,usage
 
Status
Not open for further replies.

Reply to M3/Hr gas flow rate in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
203
P
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
478
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock