does anyone know the rate for the vaillant combi eco tec plus 837 with my calculations it being a 28kw i make the m3/hr 2.6 mi's say 4.0:confused: or am i reading it wrong.
MIs state 4m3 per hour, check you have the boiler set on max rate, or check your sums!!!!!!!
easy,on full rate just time the meter,2 mins usage x 30 = m3 per hour
or do the sum again and check with a gas rate slide rule,this will give you a guide and as oldplumber advised max rate when doing gas rates, i will hazard 2 guesses either you have ccn 1 core on the way and your practising or your looking at a fault
I only use the m3/hr for pipe sizing. Use KW (gross or net) for gas rating. As said above be sure you have boiler in max setting.
i was looking at pipe sizing and divided the 28kw by the cv 10.77 gave me 2.6
So what exactly are you trying to do? Are you trying to work out pipe sizing or are you gas rating an existing appliance?
dont forget the ch output is 28kw and the hw output is 37kw, take a look at your tech data more carfully:confused: the big clue being model number of 837
Just had a look at the 837 data and Vailant dont give the inputs just the outputs and and the gas rate of:
Connected load (if needed, related to stored charge/
water heating) at 15 °C and 1013 =mbarG20: 4.0
Coley
gas rate,2 min, hot water tap on full you need to get corgi gas rate slide chart,ÂŁ9,
fga test
@old plumber
Well spotted we have just installed a ecotec too I forgot the data required was futher down.
Coley
Hi
If you log on to [DLMURL="http://www.vaillantdownloadservice.co.uk"]Vaillant Technical Download Service[/DLMURL] you can download all technical information on all Vaillant products.
"vaillant technical" is a contradiction in terms !!
vaillant librarians is a better descriription, but your on the right lines using their web service - if the page loads in less than 45 minutes your still be better off than ringing them !
if only they'd listen to people and sort their tech help side of things sorted out, they might have a chance at the future market.