18mbar.............at meter .....working pressure on boiler fine....is all ok....!
 
I would say to contact the supplier and let them know as it should really be between 19mb and 30mb but they will probebly say everything is ok or maybe send someone out. Check you manometer is zerod tho first hahaha
 
Working pressure at the meter between 19-30mbar? Think you will need to recheck those figures. :)
 
30mb. Wow. Bet you cook your eggs in no time!
 
It may be a case of a faulty governor or just resetting but in Bexhill there are issues with working pressures as low as 17 mbar at the meter. This is down to inadequately sized pipes throughout the town and when you call Southern Gas Networks out there is nothing that they can do until the gas pipes have been renewed. You have to be really fussy with pipe sizing in Bexhill as you have hardly any leeway.
 
Working pressure at the meter between 19-30mbar? Think you will need to recheck those figures. :)
eh....i am asking you...i have 18mbar at the meter when the boiler is operating,the working pressures on the boiler are fine,is it ok to use or get esp in, 3 people liked it ,strange ,please explain
 
eh....i am asking you...i have 18mbar at the meter when the boiler is operating,the working pressures on the boiler are fine,is it ok to use or get esp in, 3 people liked it ,strange ,please explain


desrob, my statement re rechecking those figures for working pressure at the meter was in direct response to hobo's quote below. I apologise if I didn't make that clear.

I would say to contact the supplier and let them know as it should really be between 19mb and 30mb


The reason three people may have like my comment is because he was not describing correct tolerance for working pressure at the meter. In fact, he is describing tolerance for standing pressure. I didn't give the full correction immediately because I was hoping that he, or any one else learning from this threads, would check their reference material.

You have now identified correct working pressure tolerances. You have found that it is below the tolerance so I personally would have turned off the meter, issued the appropriate documentation, reported it to the Grid and got a job reference number. If the Grid chose to do nothing about it, I'm not the last (wo) man on the job.
 
Last edited by a moderator:
desrob, my statement re rechecking those figures for working pressure at the meter was in direct response to hobo's quote below. I apologise if I didn't make that clear.




The reason three people may have like my comment is because he was not describing correct tolerance for working pressure at the meter. In fact, he is describing tolerance for standing pressure. I didn't give the full correction immediately because I was hoping that he, or any one else learning from this threads, would check their reference material.

You have now identified correct working pressure tolerances. You have found that it is below the tolerance so I personally would have turned off the meter, issued the appropriate documentation, reported it to the Grid and got a job reference number. If the Grid chose to do nothing about it, I'm not the last (wo) man on the job.
you'll go green...apology
accepted
 
Don't know if this is relevant but Vaillant accept 16 MBar at boiler because they've found that there is some suction via fan through the gas valve. Having it at 16 makes it really helpful on pipe sizing the gas.
 
That is low. Are they the boilers that still have aps switches on still?
 
although it is correct that some boiler manufactures now state allowable figures below 20mb for inlet pressures at the inlet side of the gas valve, this does not excuse having more than 1mb drop from the meter and the appliance as required bu gas regs. Worcester for example will allow 16.5mb on some of its boilers. Taking into account 19mb at the meter, 18mb at the boiler isolator and a 1.5mb drop (16.5mb) across the gas pipework from its iso valve to test point on its gas valve.

This is the problem with manufactures stating low figures, some engineers will use this as an excuse to ignore undersized gas carcus. The best solution would be to include a test point at the isolation valve to ensure we can be sure we have got things correct.
 
18mbar.............at meter .....working pressure on boiler fine....is all ok....!

as other have said 18mb is too low and you normally need to call the grid. This said it can be allowable to have it lower than 19mb during peak periods. which if i remember correctly (but not 100% sure if correct) is a period of no longer than 5% of the total use of the appliance. I think there may be a technical buletin about this.

call the grid and let them decide if its ok.
 
Surely if mi says lower MBar at boiler its ok. I always thought mi,s over ruled every thing else. Surely this rule only applies to appliances that state it in mi,s. Fires cookers and not anything with a zero governor.
 
Most of the stated MI relate to losses inside the applaince before test point. MI does not overide the need for correct pipe sizing and never will. Especially when more than one applaince is installed in a property.
 
its a grey area for sure, the last worcester i fitted i had a total drop from meter to gas valve inlets of 0.9mb (wp) in therory i could have allowed 2.5mb allowing for 1.5mb across the gas internals of the applaince. If i had a test point at the iso valve i could determine that any drop over 1mb was not all on pipework. I know of some engineers that will fit an test point before iso valve to allow correct measurements and peace of mind.
 
As far as I'm conerned it's quite clear for example Ideal state that the logic plus range is able to deliver it's full output at inlet pressures as low as 14mbar they also state that pipework should be fitted in accordance with BS 6891.

BS 6891 states

5.2.3 The pressure drop between the outlet of the meter and the points to be connected shall not exceed 1 mbar at maximum flow conditions.

This is not a case of MIs over riding British Standards but requiring that they are complied with. The low inlet pressures are not a get out for sloppy pipe sizing and installation but a safety net in case of low pressure problems with the supply.
 
This is the problem with manufactures stating low figures, some engineers will use this as an excuse to ignore undersized gas carcus. The best solution would be to include a test point at the isolation valve to ensure we can be sure we have got things correct.

Agreed. This is also suggested in gas safe bulitin re Worcester inlet pressure. The low pressures quoted do not mitigate the fact that only 1mbar loss is allowed over the pipework - the low figures are because the test point itself is causing a 1.5mbar loss, and therefore the supply to the appliance is actually correct,.

In theory in the event that pipework is undersized at what point would it start to affect flow rate/gas rate. I assume that as if gas demand is higher than the design limits of the pipework it will still be able to supply the required gas rate to the appliance and pressure would start to fall, until it got to the stage where the pressure was less than that required by the manufacturer before it would cause problems.
 
Last edited by a moderator:
Ok, if the mi,s state a figure and there no way or no call for it from mi,s to put a test point in. Obviously you'll test with other appliances operating and anyone who adds an appliance is responsible for correct sizing up or down stream. Mi,s do some times over rule the regs, dfe fires for example over 7 kw need ventilation unless stated in the mi,s.
 
yes i understand the argument about MI over riding the regs, but a gas carcus will in most situations have more than one appliance so cant be effected by any one appliances MI, and i think if you asked any manufacturer the opinion you will get the reply stating the same and pipework must comply to the current gas regs.

If they changed the regs then thats a different matter of course.

as reguards test point, my opinion is it would be helpful if manufactures fitted one. If on your gas safe inspection your inspector asked how do you prove the pipework has less than 1mb drop what answer would you give? a test point would help you prove this. But why would manufactures help us out?? :)
 
Last edited:
Fair one, gas regs are some times not as clear as they could and are open to interpretation . Be nice for some clear guide lines. Oh how it gives me a head ache deciphering it all.
 
The fact is it should be 19mlb min but if you make the call to get them to come and change thye gov. they may refuse as petty to them. Providing no appliances are effected and all burner and working presures are achieved dont worry about it..thats just my oppinion...
Bren.
 
Speaking to one of the ESP guys the other day, and they've got a loophole they use. They say that in a situation where work is required to the mains as long as it's 6" in old money it's passable.
 
Status
Not open for further replies.

Reply to working pressure at meter in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days it's increased whilst cold...is this a regular problem.
Replies
1
Views
175
Can anyone remember the Mira mixer shower that would work down to a really low pressure on a vented hot water system without a shower pump?
Replies
2
Views
148
Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one ....just easy to use and reliable. The fluke 115 looks good but its above my budget. My current socket and see one was great but it's developed a fault.
Replies
7
Views
264
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
170
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...