  1. Inverness

    Inverness Plumber GSR

    hi guys, went to carry out a service... went to high fire setting mode but nothing happened? Blue flashing light 5 times.. checked condensate not blocked.. flue good..
    Reset the thermostat knob but nothing happened. Standing gas pressure 25mb to the gas valve..
    When I put the heating on from the programmer the boiler fires up fine but I noticed the blue light still flashing but faster? I notice the heat exchanger was very hot to touch and making noises?

    I'm new gas engineer so be gentle.lol
     
  2. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    was the pump running?
     
  3. Inverness

    Inverness Plumber GSR

    Yeah it was pulsating and the return pipe was getting warm.
     
  4. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    port valves open ?

    o and the 5 flashes means its in service mode
     
  5. Inverness

    Inverness Plumber GSR

    Yeah the port valves open.
    I'm I right in saying, when nothing is calling for heat. And I turn the service dial to max shouldn't the boiler go to high fire?. Or do I need to go and call for the heating to cone on?
     
  6. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    pump wont run if you dont have anything on eg call
     
  7. Inverness

    Inverness Plumber GSR

    Ok I'm confused now. I took off the cover and I rotated the knob that's concealed behind the Panel and rotated it to max as it was in the normal. The boiler started to flash but never fired up? Shouldn't the boiler fire up like the chimney sweep button on the other worcesters?
     
  8. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    did it have demand?
     
  9. Inverness

    Inverness Plumber GSR

    No it didn't. I thought when you put it on max this would fire up the boiler?.
     
  10. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    no as no pump connected your thinking of a combi
     
  11. Inverness

    Inverness Plumber GSR

    Alright so if I have a demand on then put it to max I'll be able to get a negative air pressure reading.

    I'm stupid
     
    • Like Like x 1
    • Agree Agree x 1
  12. Inverness

    Inverness Plumber GSR

    Thanks Shaun
     
  13. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    :D
     
  14. king of pipes

    king of pipes Trusted Plumber GSR

    You need a external heat demand bud to get rid of the heat . Kop
     
  15. Bibbs118

    Bibbs118 GSR

    That negative fan test is bullshit, ive had it pass that test but need a full strip and clean, and fail that test but not need a strip and clean.

    Could just be me but i dont do that test, i remember when it came in and i find it proves nothing
     
    • Agree Agree x 1
    • Useful Useful x 1