Discuss Worcester G* Cdi 37kw... Luke warm DHW in the Gas Engineers Forum area at PlumbersForums.net

Hobo128

Gas Engineer
Messages
302
Hi guys...
Happy New year to you all....
Been out to a Worcester Greenstar Combi last week.... Problems with hot water not getting very hot.... Boiler is set to max on and I'm getting about 40 degree out of the tap.... Turned of the flow and return at the boiler to check diverter but this made no difference.... Should I change the plate to plate.... Thanks
 
Your return temp back to the heat exchanger (boiler)

should be at the same temp as your hot water out
 
Sorted it.... Flow rate was to high and also burner was very dirty... fan pressure test proved this.... Cleaned it and adjusted the flow rate.... seemed to sort it... thanks
 

Reply to Worcester G* Cdi 37kw... Luke warm DHW in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Morning all, I have a Worcester Bosch 8000 life 40kw boiler on system with 7 radiators and the boiler is located in the loft of a 1907 end of...
Replies
6
Views
736
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
Replies
6
Views
436
S
Morning all, I have a Worcester Bosch 8000 life 40kw boiler on system with 7 radiators and the boiler is located in the loft of a 1907 end of...
Replies
0
Views
499
Simon from Watford
S
M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently...
Replies
1
Views
420
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
289
MartinPod81
M
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock