I am trying to update an original wired Mk1 Drayton Digistat that I fitted myself as a replacement for an analogue Satchwell (or I think it could possibly have been a Honeywell) room stat in either 1993 or 1996 with a HoneyWell Chronthem CM907 Roomstat. This is the very earliest LCD digital stat from Drayton before they had several models in their digital stat range. The boiler is an oil fired boiler on an old style gravity feed system where the hot water circuit is always also heated up when the central heating is running although the hot water circuit can be heated up with the central heating circuit switched off.

In any event when I fitted the very old Drayton Digistat 15 or more years ago I was faced with a 5 wire set up on the back of the previous room stat with red, black, blue, green and yellow wires. This is because the room stat (previously I think a Satchwell) originally controlled a driven motorised valve for the downstairs heating circuit while the upstairs circuit originally had a motorised driven valve controlled by a timeclock. However the downstairs valve had failed some years earlier and the system was then modified so that the room stat now only switched on or off the heating pump. More recently the upstairs mechanical Satchwell time clock became intolerably noisy and rather than being replaced was simply disconnected by the boiler servicing engineer and the upstairs circuit valve left permanently open.

In the mid 1990s when I removed the Satchwell stat and fitted the Drayton Digistat I blanked off the green and yellow wires and connected the remaining three wires (red, black and blue) to the Drayton Digistat. However when I came to try to change the stat today the wiring to the four terminals was shielded with black electrical tape and I may not have accurately noted down which wire was connected to which terminal but definitely the Red wire was connected to Terminal 1/Live and I thought the Black wire was connected to terminal 3/Sat and the blue wire to terminal 4/N but possibly the Black wire was connected to Terminal 2/Dem but a wire was definitely connected to terminal 4/Neutral and I thought it was Blue unless the Black and Blue were the other way round.....

Trying to cut a long story short after reading up on this forum about the dangers of wrongly connecting the Neutral wire to the new CM907 and blowing it up I became scared about the risk of destroying it and so decided to put the old Drayton Digistat back for now. I hasten to add that whenever I was working on the wiring on the back of the stat I always turned off the mains supply since I acknowledge that I am not a qualified electrician, even though in theory a room stat's wiring is not much more complicated than a wall light switch.

Anyhow putting the wiring back on the Drayton Digistat I consistently kept the red wire on Terminal 1/Live but as I was having no luck making the room stat switch on or off the heating pump tried a number of combinations of the blue and black wires on terminals 2 (Dem), 3 (Sat) and 4(N). A couple of these combinations blew the 3 Amp fuse of the wall switch controlling the power to the central heating programmer and heating pump next to the boiler in the kitchen (the room stat is in the living room) and other combinations did not blow the fuse and the programmer functioned as normal but throughout the boiler would now only operate in response to demand from the hot water circuit and after the boiler had reached temperature turning up the Digistat to a level that should have caused the central heating pump to operate and make the boiler fire up failed to do so. The Digistat made the usual on/off clicks but the pump belligerently refused to cut in and then make the boiler fire as the water temperature in the boiler dropped.

Finally after trying various three wire combinations (always keeping the red wire on L but with Blue and Black on a variety of 2, 3 and 4 ) I made the probably rash decision to connect just the red wire to 1 and the black wire to terminal 3/Sat. When I turned the mains back on after this there was a nasty pop from the Digistat and a burning smell and its clear that I have fried it as all it now shows is CHECK BATTERY and replacing the battery does not help.

I accept that I may well need to get in a professional central heating engineer or electrician to finish the job but can anyone clarify whether the fact that a combination of the red wire to terminal 1/Live and just the Black wire to 3/Sat burned out the digistat possibly suggests that the Black wire is in fact the Neutral wire or is the fact that I attached the black wire to terminal 3 without also having the Blue Neutral wire attached to terminal 4 responsible for the burn out incident? I had previously had the blue and black wires attached to terminals 3 and 4 together in both possible orders and neither of these combinations burned out the Digistat.

If I go to B&Q or another DIY shed I can clearly buy some sort of mains wiring tester but other than establishing that the red wire is the live wire should I also be able to definitely establish which of the black and blue wires is Neutral and should therefore not be used with the CM907? I assume that the green and yellow wires I taped out 15 years ago are not needed as the old Drayton Digistat has been using just the red, blue and black wires to operate for all these years with no problems other than a battery change every couple of years.

I should add this room stat is on my 75 year old widowed mother's heating and hot water system so I am now severely in the dog house for screwing it up when all I was trying to do was to make the system more efficient and less hassle as the very first Drayton Digistat is a real pain because to turn the temperature down two degrees you have to cycle all the way up the high 80Fs and then roll back down to the 40Fs and all the way round just to make that small adjustment.

I know that there will inevitably be plenty of you on here now wanting to deride me for taking on this job when I am not a qualified electrician but all I can say is that I did manage to fit the old Digistat ok myself and I do take sensible precautions such as switching off the mains before i work on the wiring connected to the room stat.

If anyone can help and particularly comment on why they think attaching just the red wire to Terminal 1/L and the Black wire to Terminal 3/Sat blew it up then it would be very much appreciated.
 
I should add this room stat is on my 75 year old widowed mother's heating and hot water system so I am now severely in the dog house for screwing it up when all I was trying to do was to make the system more efficient
.

Maybe you should have spent a couple of quid getting someone who knows what they are doing.
You obviously lack the skills to work a multimeter so this may be best.
 
This question has already been asked twice (hijacked an old topic and started a new one) on another forum. Unfortunately the OP does not understand the KISS principle.;)
 
OK let me try to simplify.

I took off an old room stat (Drayton Digistat very earliest ever digital model) which had a messy load of wiring behind it and several taped off out of use terminals including green and yellow wire and redundant red and black wires. Some of the wires appear in a grey 13amp ring main type sleeve (mainly the taped off wires apart from the black wire that seems to actually be a neutral) while the red and blue wires appear on their own and do not come out of the grey plastic sleeving.

The bottom line is that only the red, black and blue wires were attached to the old Drayton Digistat (there are also out of use red and black wires that are taped off). The red wire is definitely live so the only confusion is about the black and blue wires with the blue seemingly being the switched current path to the heating pump and the black wire probably the neutral, despite the colours.

So how do I test to make sure which is which. I think I need to attach the red wire to terminal A and the blue wire to terminal B on the Honeywell Chronotherm CM907 but I am not 100% sure it is the blue and it could be the black wire. Making a mistake will write off the Honeywell CM907.

How do I test to see which wire is the neutral and which is the switched live from the heating pump circuit without blowing anything up? I have a basically logical brain and would never touch bare wires while the mains was switched on but clearly I am not a trained electrician even though I do understand some of the basic principles of an electrical circuit.

Can someone tell me what sort of testing meter I should buy at a DIY shed and what tests I need to run on the wires to establish which is which?

Also what is the proper use of terminal C on the Honeywell Chronotherm CM907. I believe that in this application it should not have any wiring attached to it and there is no Neutral terminal on the Chronotherm CM907.

Anyone else have any useful advice to offer on this as its now quite urgent.
 
Last edited by a moderator:
Anyone else have any useful advice to offer on this as its now quite urgent.

Yes,get someone in who is qualified to carry out the works because from the post above you have made it clear,you have little ,if no experience or knowledge in the electrical department,You could cause a lot of expensive damage to your heating system controls.Sometimes you have to know when to step back and this is appears is one of them,look up electrical fires on the net and imagine you are sat in the middle of one of them,not a nice thought,be responsible and put your diy tools away and get someone in
Can not see you being given any better useful advise were ever you have posted


imho
 
Last edited by a moderator:
I've got some wiring experience having done a course at college, and from what you've said in both posts it doesn't make much sense. I would've admitted to myself long before hand I was out of my depth and got someone else in. You should do aswell.
 
diy ers and wiring = honeywell stats welded to ceiling honestly mate just get someone in who knows how to do it,as you clearly dont messing with electrics at best could give you pointy hair and a permanent stiffy at worst death
 
diy ers and wiring = honeywell stats welded to ceiling honestly mate just get someone in who knows how to do it,as you clearly dont messing with electrics at best could give you pointy hair and a permanent stiffy at worst death

Problem is GM, the poor sod he gets in is gona be left staring at 4wires wondering which one is which and which wire was in which terminal before the "diy" began. Notice the inverted commas at diy. I would call this plain stupidity, If wacky races got myself or one of the other boys in here in to do the replacement it would have been finished within half an hour and his family wouldnt have had to do without heating for however long. He gets no sympathy from me
 
Status
Not open for further replies.

Reply to Wiring Difficulties Replacing Digistat with Honeywell Chronotherm CM907 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock