Just had a WB combi installed and went for their Wave controller, a feature of which is weather compensation.

Enabled weather compensation during the day yesterday when the temp setting was 14C. Actual inside temp was 19C, and outside was 11C.

I understand (well, perhaps that's over-stating it a bit) that it works by monitoring the water flow temp vs outside temp, but was a bit bemused that the combi's pump runs all the time, with the boiler firing so infrequently that it's basically circulating cold water.

Is that how it's supposed to work - will the pump run 24/7 with weather comp enabled? Seems a bit of a waste of 'leccy.
 
Just had a WB combi installed and went for their Wave controller, a feature of which is weather compensation.

Enabled weather compensation during the day yesterday when the temp setting was 14C. Actual inside temp was 19C, and outside was 11C.

I understand (well, perhaps that's over-stating it a bit) that it works by monitoring the water flow temp vs outside temp, but was a bit bemused that the combi's pump runs all the time, with the boiler firing so infrequently that it's basically circulating cold water.

Is that how it's supposed to work - will the pump run 24/7 with weather comp enabled? Seems a bit of a waste of 'leccy.

Hi make sure set up of control is correct,not being wb fan, but it could be faulty flow switch on boiler causing pump over run,or software fail causing pump over run,it depends on how wb flow sensor works,I might be off target but that's what can happen on certain brands of boilers,also check set back temps on control but like last post prop needs setting up
Let us know how u get on
 
Thanks - you both may well be correct, but there isn't an awful lot of options in the set-up.

There also isn't much on the Internet about weather comp, and some forum discussions end up in fierce arguments! They do talk about things like "constant circulation" which appears to be what's happening in my case. I can easily visualise how it would work well with underfloor heating, but not so with radiators.

Maybe the system learns over time and I just need to leave it alone. In the meantime I've email WB for their comments.
 
Well, response from WB is exactly as I'd garnered from various web sources - "during weather compensation the pump will run all the time so that the boiler can monitor the temperature coming back from the rooms and maintain the calculated flow rate."

Perhaps I'm missing something but when the current programmed room temp is way below the actual temp, it's not cold outside and the outside temp is steady, it seems a bit ridiculous to be circulating cold water. I wonder how long the pump will last? :)
 
Has an external temperature sensor been installed?

No - but...the Wave unit is connected to the internet and it looks up the external temperature from a local weather station. Seems accurate enough - it knew it was 11C outside on Saturday when I was trying it.
 
probably find the internet and real life dont agree all the time, most inefficient way of monitoring outside temp you can possibly think of, swap it for a sensor on the wall of your house, then things may start to work better.
 
probably find the internet and real life dont agree all the time, most inefficient way of monitoring outside temp you can possibly think of, swap it for a sensor on the wall of your house, then things may start to work better.

Checking your local weather station My Local Weather - Your local UK weather page is probably as good as any other way to be honest. I've got a wireless thermometer using an outside sensor on my desk and that over-reads by 2C compared to an outside thermometer.


Anyway, that doesn't appear to matter in the way the system works - WB say the pump will run all the time.
 
Checking your local weather station My Local Weather - Your local UK weather page is probably as good as any other way to be honest. I've got a wireless thermometer using an outside sensor on my desk and that over-reads by 2C compared to an outside thermometer.


Anyway, that doesn't appear to matter in the way the system works - WB say the pump will run all the time.

What? How the hell is that compliant? Yes it's an A rated boiler it's hot weather comp and yes the small energy savings we make are almost instantly eaten by the pump running 24/7
 
..the small energy savings we make are almost instantly eaten by the pump running 24/7

There is a mode where the pump will turn off overnight, but oddly, not at other times when it would seem not to be required.

You've hit on the key question though: Would the gas saving by using weather comp be wiped out by the extra electricity cost (and maybe replacing pump if it wears out :) ).

I have no idea of the answer to that. Viessmann, who seem to be regarded as something of a reference point in these matters, talk about a 20% saving.
 
There is a mode where the pump will turn off overnight, but oddly, not at other times when it would seem not to be required.

You've hit on the key question though: Would the gas saving by using weather comp be wiped out by the extra electricity cost (and maybe replacing pump if it wears out :) ).

I have no idea of the answer to that. Viessmann, who seem to be regarded as something of a reference point in these matters, talk about a 20% saving.
That makes no sense to me there is no need what so ever for the pump to run continuously in order to take advantage of weather compensation as the boiler should only have to moniyor the return temperature when the room thermostat says there is a heating demand. At which point as I understand it it will set its modulation point based on the external temperature the intended room temperature and the returning temperature from the circuit. Surely the minute the room stat is at temp the boiler ceases to give a $hit what any temperatures are.
 
That makes no sense to me there is no need what so ever for the pump to run continuously in order to take advantage of weather compensation as the boiler should only have to moniyor the return temperature when the room thermostat says there is a heating demand.

It doesn't make sense to me either - I can only guess that the idea is that the building doesn't get too cold so when there is a call for heat it recovers fairly quickly. The way it works makes sense with underfloor heating where the response time would be slow, but not with radiators.
 
It doesn't make sense to me either - I can only guess that the idea is that the building doesn't get too cold so when there is a call for heat it recovers fairly quickly. The way it works makes sense with underfloor heating where the response time would be slow, but not with radiators.
Is the burner actually lit during the pumps running? It could be that its actually still circulating water through the system as long as it is still warmer than the room temperature. I would still suspect it to either not be set up appropriately or actually have sone kind of fault. The problem however is how on earth are you meant ascertain if its operating correctly. I am all for this kind of sophistication but giving the boiler tge ability to decide for itself what it needs to be doing is going to make diagnosis of sofware or component faults almost impossible without car style idb diagnostic data connections.
 
Weather compensation with constant circulation is standard practice in Europe, particularly Germany. It is also becoming popular in the USA.
 
Is the burner actually lit during the pumps running? It could be that its actually still circulating water through the system as long as it is still warmer than the room temperature.

In the time I tested it - a few hours on Saturday afternoon - it fires the boiler very occasionally. Whether that's as a result of some clever calculation it's doing, or it's merely to maintain the minumum flow temp (which I think is 20C) I have no idea.
 
Weather compensation with constant circulation is standard practice in Europe, particularly Germany. It is also becoming popular in the USA.

That's my understanding too. After some heavty duty Googling. I've found that the WB Wave controller, while new in the UK, has been sold in Europe for some time.

As I mentioned earlier, the way it works (constant circulation) makes sense with underfloor heating - maybe that's more common elsewhere. It does have a setting to choose your type of heating though - have that set as radiators.
 
There is a mode where the pump will turn off overnight, but oddly, not at other times when it would seem not to be required.

You've hit on the key question though: Would the gas saving by using weather comp be wiped out by the extra electricity cost (and maybe replacing pump if it wears out :) ).

I have no idea of the answer to that. Viessmann, who seem to be regarded as something of a reference point in these matters, talk about a 20% saving.

Really based on what?
 
Weather comp in domestic is no saving when you factor in cost of installing and cost to run
 
Sounds like it's working how it should do. With an outside temp of 11℃ and indoor set of point of 19℃ it has calculated that you only need a low flow temp to maintain the house temperature so the pump will run and the burner will fire only occasionally to top up the heat but the pump continues to circulate. Note that if you switch off the weather comp the control is load compensated so it continue to perform similar calculations using the indoor temperature.
 
Are they installing the new lower ratio burners to the new boilers yet ??

This situation could be made a lot better if the boiler could fire for longer periods at a lower burn.

PS pumps don't fail because they run but normally because they turn on & off.
 
Sounds like it's working how it should do. With an outside temp of 11℃ and indoor set of point of 19℃ it has calculated that you only need a low flow temp to maintain the house temperature so the pump will run and the burner will fire only occasionally to top up the heat but the pump continues to circulate.

The indoor set point was 14C (effectively an "off" period), actual indoor temp 19C.

I did wonder if setting the "off" temp lower would make any difference, but based on WB's comments, it doesn't matter what I do, the pump will run all the time (can be made to go off overnight though).

Note that if you switch off the weather comp the control is load compensated so it continue to perform similar calculations using the indoor temperature.

I'm not aware that WB's Wave does that unless weather comp in enabled. They told me it disables the boiler flow temp knob setting.
 
Not so! keep it simple, it cost me £20 + 1/2 a reel of 1.5mm 3 core flex.

OK, the WB Wave is dear, but we got it because I like that kind of techy thing and the ability to turn on and off remotely is pretty neat. The installer had a wobbly when I suggested Nest and I looked at Wave and it seemed OK (and it is, apart from me not understanding weather comp).

Once you've got Wave there's no other capital or install cost for weather comp - you just enable it in the app. The cost you do have is in running the pump (and the boiler PCB at times when it should be on standby) so perhaps an extra 8 hrs a day (it can be shut down overnight). Maybe a Kwh extra per day? Plus a bit of gas for the apparently random firing it's doing.
 
Last edited:
If WB have fitted one of the newer multi speed pumps it is likely to be around 5 Watts/h.

The main consideration with this is the level of insulation (i.e. heat loss), a modern well insulated & that small amount of topping up is all that is required to keep the internal temp up & the heat input is not wasted.
Whereas & old style poorly insulated place & you are better off letting the internal temp drop right down if you are not there or if you are working, as the rate of loss will slow as the temp difference gets closer. IMHO

P.S. Mr WB why do you have to be a heating engineer to under this stuff ?? I am a just poor lonely Plumber but think I have a handle on it.
What we need is better educated & qualified engineered covering all relevant fields not a dumbing down into plumber or heating or ???? or ?????
(except bathroom fitters, we can exclude them as it is such a low skill set anyone can join)
 
If WB have fitted one of the newer multi speed pumps it is likely to be around 5 Watts/h.

Sadly the boiler fitted doesn't have a modulating pump - my fault, really, I thought about it too late. Some better guidance from the fitters would have been welcome though.

The main consideration with this is the level of insulation (i.e. heat loss), a modern well insulated & that small amount of topping up is all that is required to keep the internal temp up & the heat input is not wasted.
Whereas & old style poorly insulated place & you are better off letting the internal temp drop right down if you are not there or if you are working, as the rate of loss will slow as the temp difference gets closer. IMHO

I'm not a fan of (almost) sealed boxes and it seems to me that once you start cracking open windows then all bets are off. Having the system trying to maintain background warmth while people are in and out of the house, doors open etc, during the daytime seems futiile.

P.S. Mr WB why do you have to be a heating engineer to under this stuff ?? I am a just poor lonely Plumber but think I have a handle on it.
What we need is better educated & qualified engineered covering all relevant fields not a dumbing down into plumber or heating or ???? or ?????

Certainly, as I mentioned in my other thread, it's a bit disconcerting when the (WB accredited) fitters think the sign of a successful install is when the return quickly gets to the same temp as the flow.
 
Last edited:
Sadly the boiler fitted doesn't have a modulating pump - my fault, really, I thought about it too late. Some better guidance from the fitters would have been welcome though.

Certainly, as I mentioned in my other thread, it's a bit disconcerting when the (WB accredited) fitters think the sign of a successful install is when the return quickly gets to the same temp as the flow.
Sad but true I am afraid the quality of plumbers (or heating engineers) is not what it should or could be but then you only have yourself (the general public) to blame !!!!

No one is interested in have a proper licensing system for us coupled with proper training.

Everybody seems to think they can do it, its easy, all push fit fittings & flexible cons, the physical installation may have got easier but the knowledge & technical understanding required has most certainly not.
 
Everybody seems to think they can do it, its easy, all push fit fittings & flexible cons, the physical installation may have got easier but the knowledge & technical understanding required has most certainly not.

To be fair, the plumbing they've done is neat (I visited while the floors were up). They worked quickly and cleanly. System works and the house is lovely and warm. I'm sure 95% of customers would be delighted. Indeed, I'm not unhapppy, I just think they missed an opportunity to make the most of the installation.
 
Status
Not open for further replies.

Reply to Weather compensation - pump runs all the time? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
421
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock