Discuss Was this lift system designed properly? in the USA area at PlumbersForums.net

Messages
1
I am looking to purchase a home in Colorado. It has a septic system with a lift system installed in the basement. We had the sewer line scoped and found interesting things. I am trying to determine if the force main line was installed properly (or not).

During the inspection, a scope was run from the cleanout port towards the house. The slope was positive for about 14', then started transitioning to a negative slope (i.e., uphill from the house). Near 20' in, standing water was found and continued until the scope reached a stopping point. The scope was run approximately 94' before hitting an obstruction, which was likely the force main line. Unfortunately, you couldn't really see anything because there was water in the line, so we have to assume it was the force main.

So, the question arises - shouldn't the force main line have been run until it reached the negative slope in the sewer line(i.e., downhill to the septic system)? And wouldn't it have been better to run it all the way into the septic tank (approx. 150' from the house)?

thanks!
 

Reply to Was this lift system designed properly? in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
243
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
264
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock