You do realise that extra 15 degrees is wasted energy/ warming the return up so not required

Does the boiler pump manage the load eg heats all of the rads etc ?
 
You do realise that extra 15 degrees is wasted energy/ warming the return up so not required

Does the boiler pump manage the load eg heats all of the rads etc ?
Is 60degC the ideal flow temp?

I need to check all rads when just on boiler pump, I had checked earlier downstairs and a few in the 1st floor but not all of them and not the loft rads
 
Well ideally your return needs to be below 50 for condensing boilers to be happy and with sensor mad vaillants this is a must also with your split as it won’t reach max burn / temps unless the split and temp rise is within spec (split is the difference between flow and return ideally 20dc)
 
Well ideally your return needs to be below 50 for condensing boilers to be happy and with sensor mad vaillants this is a must also with your split as it won’t reach max burn / temps unless the split and temp rise is within spec (split is the difference between flow and return ideally 20dc)
Thanks. I’ve turned down flow to 65dC and will see how that goes.

Do you have any thoughts on replacing hive controls with one that can modulate the boiler better and set different flow temps for hw/ch?
 
Thanks. I’ve turned down flow to 65dC and will see how that goes.

Do you have any thoughts on replacing hive controls with one that can modulate the boiler better and set different flow temps for hw/ch?

There brilliant and priority hot water and wc heating but you will have cooler rads then stock temp etc
 
There brilliant and priority hot water and wc heating but you will have cooler rads then stock temp etc
Thanks. Vaillant controls are a bit of a mine field, not sure exactly what I would need? Vr66 wiring centre, weather comp sensor, not sure of which thermostats for both floors and then how to incorporate a vr10 sensor for dhw temp.

Hw priority would be great, can set flow at higher temp for quicker recharge
 
Last edited:
Thanks. Vaillant controls are a bit of a mine field, not sure exactly what I would need? Vr66 wiring centre, weather comp sensor, not sure of which thermostats for both floors and then how to incorporate a vr10 sensor for dhw temp.

Hw priority would be great, can set flow at higher temp for quicker recharge
Are you thinking of not re installing the LLH?.
How are the rads performing now at 65C??, if the return is like the previous 47C then you will be getting reasonable condensing and you may be able to further reduce the target temp. Are you still just running one zone at the time with d.00 set to 20kw or both with d.00 set to 30kw or whatever?.
 
Are you thinking of not re installing the LLH?.
How are the rads performing now at 65C??, if the return is like the previous 47C then you will be getting reasonable condensing and you may be able to further reduce the target temp. Are you still just running one zone at the time with d.00 set to 20kw or both with d.00 set to 30kw or whatever?.
I’m thinking of leaving it for a bit as it is and see how it goes. Rads seem to be performing fine at 65c, don’t want to reduce anymore as cylinder heat up times will need to be increased hence the thought of changing controls for hw priority on a higher flow temp. Still running d.0 at 20kw and single zone at a time
 
Given how much is being being built on the assumption, I'd want to check (using a stopwatch) and the gas meter, that the power the boiler claims to be delivering to the system matches the amount of gas being consumed.
 
Re install LLH.

Move second filter from primary flow to secondary return in to LLH.

Set secondary pump to constant. You want LLH flow in/out to be the same to prevent return water mixing. Can roughly check with temp probes on all LLH connections.

Set boiler to auto, not limited.

Get a vaillant LLH sensor (ntc) and attach to LLH and boiler.

Set to 65c, ensure return is low enough to condensate.

Forget about it and spend your energy somewhere else :).
 
With respect to the Header, from the photos posted, that will probably have a high parasitic flow. I would have expected to see a Header with an oversized primary flow and oversized secondary return.

The term often used is Low Loss Header, the configuration posted gives hydraulic separation, but it is unlikely to be low loss
 
Re install LLH.

Move second filter from primary flow to secondary return in to LLH.

Set secondary pump to constant. You want LLH flow in/out to be the same to prevent return water mixing. Can roughly check with temp probes on all LLH connections.

Set boiler to auto, not limited.

Get a vaillant LLH sensor (ntc) and attach to LLH and boiler.

Set to 65c, ensure return is low enough to condensate.

Forget about it and spend your energy somewhere else :).
Hi

There is no filter on the primary flow, it’s a deaerator - spirotec rv2

For the pump speed do you mean constant speed or pressure?

The LLH sensor, is that the vr10 and does it need to go on primary flow on secondary flow?

Also would moving down to a 24kw boiler be ok?

Thanks in advance
 
Last edited:
With respect to the Header, from the photos posted, that will probably have a high parasitic flow. I would have expected to see a Header with an oversized primary flow and oversized secondary return.

The term often used is Low Loss Header, the configuration posted gives hydraulic separation, but it is unlikely to be low loss
Hi there

The primary and secondary flow & returns are all 28mm up the point where they branch off to the 3 zone valves down to 22mm
 
Hi

There is no filter on the primary flow, it’s a deaerator - spirotec rv2

For the pump speed do you mean constant speed or pressure?

The LLH sensor, is that the vr10 and does it need to go on primary flow on secondary flow?

Also would moving down to a 24kw boiler be ok?

Thanks in advance
NO LLH now?
Can you set d.00 to auto, and put both zones in service until fully heated up, say 30/40 minutes and with the boiler target temp at 75C, then note the flow/return temps, d.40&d.41., that will give useful info, IMO.
 
NO LLH now?
Can you set d.00 to auto, and put both zones in service until fully heated up, say 30/40 minutes and with the boiler target temp at 75C, then note the flow/return temps, d.40&d.41., that will give useful info, IMO.
Hi john

Haven’t got around to refitting LLH yet, but I’ll set to auto and report back temps

I may wait and get rgi to do it as I need to swap boiler out. The reason for the 624 was I’ve got access to a 3yr old one from a friend who’s removed it for a combi
 