jillycee

Hi, We ran out of oil yesterday and have had a delivery today, however the boiler will not re-start. Any ideas?
 
look on the fuel pump for the letter p put an allen key in the allen screw and lossen until you get fuel oil out of it tighten it back up and re start the boiler with the reset buton on the burner
 
As per Fireblade's comment but you'll need a fair amount of oil coming out as there'll be some in the burner and pump already. If there's a long sticky outy thingy on the left of the burner (a hexagon shape with a round black piece in it) you can bleed the oil from here using a 4mm allen key and kitchen towel.
 
Hi, Heating and water back!!! Many thanks for all of your help
 
Status
Not open for further replies.

Reply to Urgent help needed to re-start Mistral oil combi boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
200
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
250
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
197
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock