Hi there,
Third call back today. Bit of help please. Installed Telford easy fit unvented cylinder 3 weeks ago. Over heat stat has started tripping on cylinder leading to no hot water. Primary circuit for the coil set at 73*C so no where near manufacturers cut out temp of 83*C.

When I'm there and have the hot water on if I turn the cylinder stat down it closes the 2 port valve and turns the boiler off so it's wired in correctly and that side of it is ok.

Presuming it's a faulty stat but just wondering if there's anything I might be missing???

Cheers
 
You set the hot water temp to 73 ?
 
Not the cylinder stat. That's set at 65*C. I'm taking about the temp for the flow on the boiler being set at 73*C. The cylinder stat sits next to the coil in the cylinder.
 
Bring the cylinder stat down to 60 should sort it
 
My thoughts also too high a temp lower it to 60 and try that go to 65 max
 
What's the temperature of the water at a tap, assuming it doesn't have TMV at cylinder?

If the stat is low down in the cylinder even 60 is too high.
 
Thanks guys,

No TMV fitted. I'll try nudging the cylinder stat down and making sure the DHW outlets are achieving 60*C minimum.

I think I'm over thinking this one a bit. Either a faulty stat or cylinder temp set to high.
 
Thanks guys,

No TMV fitted. I'll try nudging the cylinder stat down and making sure the DHW outlets are achieving 60*C minimum.

I think I'm over thinking this one a bit. Either a faulty stat or cylinder temp set to high.

Store temperature should be 60°C. Outlet temperatures (assuming you mean taps) need to be 50°C within one minute. See:

HSE - Legionnaires' disease - Risk systems - Hot and cold water systems

for the details.

If you have G3 ticket, you should know this stuff in detail already. If you don't have a G3 ticket you're breaking the law by working on unvented systems.
 
Chuck everyone here knows the basics of what temp stored hot water should be at. The thread is about the problem with the stat.
 
  • Like
Reactions: deg
Status
Not open for further replies.

Reply to Unvented over heat stay tripping intermittently. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
397
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock