J

JSlippy

We’ve had a UFH system installed as part of our home renovation which is run alongside our existing radiators. Some of it is in rooms with LVT flooring which means we’ve got to be careful with water temperature (floor temp limits are set, but can easily overshoot if water is too hot).

Our problem is that sometimes the mixing valve shuts the flow down completely even when the UFH pipes are cold. Today our lounge wasn’t warming up so I checked the system. The pump was running but all flow meters were at zero. The temperature going into the manifold was about 30 degrees, but the return temp from the manifold was about 40.

Presumably the mixing valve closed completely when the return temperature reached 40 degrees. But because the valve is closed, it can’t detect when the water in the UFH pipes falls (for example if a different room calls for heat).

I turned the mixing valve setting from 4 to 6, which instantly sent flow through the system and the return temperature dropped like a stone! I was able to drop the valve back to 4 and it worked as normal.

Surely this isn’t the way the system is supposed to work. I understood that the mixing valve was supposed to blend water from the boiler with the manifold return, but keep water flowing through the UFH pipes the whole time. That clearly isn’t happening here, does that indicate a problem with the way the system is set up?

The pump is a Grundfos UPS3, mixing valve is ESB VTG141. We can get the installers out but there's no chance I'll be able to replicate the problem for when they're here! If anybody has any tips on whether this is expected behaviour or what should really be happening, it would be appreciated!
 

Reply to Underfloor heating mixing valve issues in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
184
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
445
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock