Messages
1
Downstairs I had a 12 port Hetta underfloor system installed by a plumber. Upstairs I installed an 8 port Hetta system myself using the existing pipework which had an old system on. Both systems are now fully Hetta with exactly the same components on (wiring centre, manifold, actuators, wireless stats).

The Hetta actuator has a clip on the plunger which you remove when you have attached them to the manifold which I did upstairs and it pushes the pin down closing the loop. When I call for heat the plunger pops up and you start to feel heat in the pipe. Stop asking for heat and the plunger goes down as it should.

Downstairs however the actuators have all got the clips still attached which means the plunger is in the open position so when one zone is calling for heat all the zones get heat however when I tried to remove the clips the Hetta wiring centre doesn’t open the actuator so all the zones get heat except the one that is calling for it. Even when the particular zone is turned off the plunger doesn’t go all the way down so I’m wondering why there is a difference and what can I do about it? It is happening with all the actuators on all the zones even if I swap them with actuators off my upstairs underfloor this discounting any possible issue with tue actuator. It can’t be very efficient filling all the zones with heated water every time one zone is calling for heat?

Has anybody experienced anything like this before?
 

Reply to Underfloor actuators working on one system but not on another? in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
191
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock