But every single calculation is an approximation and gas assumptions. Even calculating the area if a circle is an approximation and has a been rounded up or down. Pi, is an irrational number and cannot be expressed as a fraction so nothing is 100% accurate. Fluid dynamics is based on tensor calculus which is fraught with approximations.


Heating systems can be designed very well with rule of thumb and a rudimentary model. A real model would be immense and require a super computer.? Lorenz had some very interesting thoughts on chaos. If you make a cup of tea u upset the thermal drifts and how a radiator works I some one else's house 120miles away in 3 days time!


When you have designed and installed a system you can check it's performance. Set rooms and flows so you get delta t of rads and 22c drop at boiler and cylinder on full tilt few measurements and bobs your uncle

SBEM calculations were tallied against loads of new builds and were within 5% of actual. This was done before BREEAM and it shows that calculations do work and that you should at least think about what your doing before just doing it?!!!!!

Bugger me Erm have you been knocking about with Chris Watkins
 
if you look at the domestic heating design guide as a general guide as many do in the industry you will find a table that they have recommended allowances for certain sized cylinders.

for example's

120l cylinder requires aprox 7.2kw to heat up in one hour (10-60) and suggests an allowance of 2.0kw when sizing your boiler.

225l cylinder requires aprox 13.0kw to heat up in one hour (10-60) and suggests an allowance of 3kw when sizing your boiler.

we all understand that modern cylinders have high recovery/high kw coils which can re heat the cylinders in 15 mins. But i would think that if your cylinder needs to recover in this time frame its prob undersized or not correct for use. I would say that if you wanted to be over cautious you may make an allowance for about half the cylinder rated kw in your calculations as suggested to shef by RM. But this could still be over the top really.
 
But every single calculation is an approximation and gas assumptions. Even calculating the area if a circle is an approximation and has a been rounded up or down. Pi, is an irrational number and cannot be expressed as a fraction so nothing is 100% accurate. Fluid dynamics is based on tensor calculus which is fraught with approximations.


Heating systems can be designed very well with rule of thumb and a rudimentary model. A real model would be immense and require a super computer.? Lorenz had some very interesting thoughts on chaos. If you make a cup of tea u upset the thermal drifts and how a radiator works I some one else's house 120miles away in 3 days time!


When you have designed and installed a system you can check it's performance. Set rooms and flows so you get delta t of rads and 22c drop at boiler and cylinder on full tilt few measurements and bobs your uncle

SBEM calculations were tallied against loads of new builds and were within 5% of actual. This was done before BREEAM and it shows that calculations do work and that you should at least think about what your doing before just doing it?!!!!!

after my head hurt trying to understand your post it all boils down to the bit in red :)
 
if you look at the domestic heating design guide as a general guide as many do in the industry you will find a table that they have recommended allowances for certain sized cylinders.

for example's

120l cylinder requires aprox 7.2kw to heat up in one hour (10-60) and suggests an allowance of 2.0kw when sizing your boiler.

225l cylinder requires aprox 13.0kw to heat up in one hour (10-60) and suggests an allowance of 3kw when sizing your boiler.

we all understand that modern cylinders have high recovery/high kw coils which can re heat the cylinders in 15 mins. But i would think that if your cylinder needs to recover in this time frame its prob undersized or not correct for use. I would say that if you wanted to be over cautious you may make an allowance for about half the cylinder rated kw in your calculations as suggested to shef by RM. But this could still be over the top really.

9kw for a 180 may be on the high side,i can see what where they are coming from
 
So if I went and turned off your central heating, and switched the entire output of your boiler to hot water,without touching the rads, how many minutes would it be before you started to notice purely from detecting the drop in air temperature?

20mins? 30mins? Well, blow me, the cylinder is fully recovered, so lets heat those rads back up.

And that would only be an issue when it was freezing outside and someone had drained your entire 210 litre cylinder.

Under more realistic conditions, the cylinder would have recovered in less time than it would take to brew up a cuppa.
 
At the very best, you are covering your bum against claims by being able to prove that your system was designed to best practice. That may be a worthwhile aim, but lets not pretend its engineering.
Reminds me of the way the Gas Board (as it was pre privatisation), when they had the monopoly, used to advertise heating systems with "Guaranteed Temperatures". All they did was install oversized rads and an oversized boiler. No heatloss calculations - just a rule of thumb, which some online calculators still use: room volume in cu ft x 5 (if I remember correctly) gave you the BTU required. I remember picking up a radiator manufacturer's leaflet at B &Q in the late 80's which had this formula on it.
 
New posts
Status
Not open for further replies.

Reply to under sized boiler ??? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all Having some renovations done on ground floor and looking to get rid of / replace some of the older looking boilers on that floor (mainly...
Replies
16
Views
2K
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
Hi All, I'm trying to work out a boiler size for a huge, four storey victorian property, part of which is already heated. I'll be adding a second...
Replies
1
Views
2K
Hi, After a bit of a saga with my plumber, I need to chose boiler size as soon as possible, the plumber is not going to do any heat loss...
Replies
16
Views
3K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock