C

Cold fish

Hello, just bought a new house in December, UFH gas boiler on ground floor. Open plan living area. Thermostat set on max (26), room temp is 16. Just paid extra £500 for extra accelerator pump. Still floor is stone cold, except one third of kitchen floor. Previous owners had system flushed 6 months ago. Any suggestions would be much appreciated, is ruining life in the
new house as can't sit downstairs !
 
How old is the house?
Was the U-F fitted when the house was built?
If not how old is U-F?

Where was this expensive pump fitted?
 
Zone valve could be faulty if one is fitted. If its a Honeywell it can be manually opened. Also check pump is spinning.
 
Hello, thanks for your replies. House is 15 years old. Suppose UFH was installed at that time. New pump is a grundfos pump. Temp gauge on manifold says 40, the return is 30.
 
I am no expert, could not really explain technically. It is just next to all the blue pipes that go off into the living room etc. I can hear it is working but does not feel boiling hot. Plumber said it would definitely solve the cold problem but 24 hours later still 16 degrees.
 
I live in hope.....can't wait for the summer as feeling obsessed about how cold it is. Shame can't just put radiators instead.
 
Also sounds like air lock on one of the circuits as mentioned before. How many pipes on the manifold ?
 