Hello

As per title, the 3 zones of UFH to one manifold are not working.

All is good from an electrical perspective, i.e. the room thermostats are calling for heat, the UFH wiring centre is triggering the boiler, but simply no heat is coming from the floor.

What makes analysis difficult is 1) recently moved in and had the system turn off for long period whilst doing works 2) 2 of the zones are same room, large kitchen with aga oven releasing heat.

Assuming it's an issue at the manifold, what are the things I can test for? The flow meters are gunked up, could that be the cause or indicate whole system needs power flush? It has a grundfos motor but I can't hear anything, but same motor is on different manifold and is silent but working fine, how do I test if motor actually working?

Anything else I can cross off before getting someone out?

Thanks!!
 
No you are correct but the flow meters look shut there eg not much gap between need to close two and one open

Ignore me just noticed the pumps pumping down / into flow meters
 
Last edited:
No you are correct but the flow meters look shut there eg not much gap between need to close two and one open

But I looks like your manifolds are the wrong way round eg flow meters should be top unless the top valve is the flow ?
Honestly I don't know. There are no obvious markings other than on manifold it says brand name and IN and OUT which I assume resembles flow/return. In which case the red sticker at the bottom has IN.

Worth me flipping these around and put actuators at bottom?
 
For reference this is the upstairs manifold which is working broadly as intended (although one zone gets too hot and another not enough, I also note no isolation valve for flow/return)
20211208_133130.jpg
 
Does the closest one to the pump get the hottest / too hot ?
 
I've ordered a digital thermometer (coming tomorrow) as to my touch there is very little difference in the metal part of manifold ie top and bottom bar both hot. Pipes are room temperature coming out from either flow or actuators part
 
Open one flow meter fully open
 
Thats what I've done so far. Opened one fully, closed two fully, given it some time but nadda. Same for all three loops.

I'm confused how both top and bottom can be hot if loops themselves aren't flowing. I thought only flow side was fed the warm water from the flow mixer. From the piping on mine it looks like there is a connecting (vertical) pipe from the flow mixer that is perhaps simultaneously feeding both top and bottom bars
Open one flow meter fully open
 
It could be that you have inadequate flow to your actual manifold, your main system pump could be the issue. Isolate the other manifold that is working and see if it gives an improvement.
 