I have checked with the grundfos replace app and it has highlighted the ups3 as a direct replacement for my existing grundfos 15-50x18. if the outputs are matched wouldn't I still have the same problem?
If you post a close up photo of your pump then might be able to get the pump curves but as pointed out above it will only pump the same volumes of water at a much lower head than the UPS3 so far less need for balancing/tweeking lockshield valves if UPS3 installed.
The UPS3 is a direct replacement but you would have to choose different pump curves to give the lower head that your pump is pumping presumably on speed 3?.
 
If you post a close up photo of your pump then might be able to get the pump curves but as pointed out above it will only pump the same volumes of water at a much lower head than the UPS3 so far less need for balancing/tweeking lockshield valves if UPS3 installed.
The UPS3 is a direct replacement but you would have to choose different pump curves to give the lower head that your pump is pumping presumably on speed 3?.
This is the Pump I have at the moment and you're right it is on speed 3
 

Attachments

  • 20230314_124843.jpg
    20230314_124843.jpg
    343.6 KB · Views: 22
You have done well Kevin, that pump was built in week 34 2000 I think so 23 years, not bad but only a minnow compared to the UPS3., immediately below, which will pump 1.7m3/hr at a 5M head if required, the selectric will only pump that at a 3.3M head.

1678807682243.png


1678807532097.png
 
You have done well Kevin, that pump was built in week 34 2000 I think so 23 years, not bad but only a minnow compared to the UPS3., immediately below, which will pump 1.7m3/hr at a 5M head if required, the selectric will only pump that at a 3.3M head.

View attachment 82073

View attachment 82072
that could well explain things. the house was actually built in 2001 as a 3 bed with a lounge and kitchen. I purchased it in its current state, 5 bed and 4 reception (includes a big conservatory with two big rads) in 2015. Lots of additions, but no update for the pump.
Looks like I will be replacing the pump and trying that.
thanks for the help, if it doesn't cure the problem don't know what I'm going to do!
Here's hoping
 
You will be lucky if the O rings dont leak on the ball valve spindles. You might find it easier as well to just cut across the securing nuts ( at the two slots) with a junior hacksaw to remove them, if the O rings don't leak you can just buy replacement nuts, they have two slots like in the photo and you can slip them on over the valve flanges, also use rubber gaskets.
 

Attachments

  • Pump Isol Valve Nut.jpg
    Pump Isol Valve Nut.jpg
    196.4 KB · Views: 14
Update:

Fitted New ups3 pump, as predicted the valves leaked through the o rings, but luckily I had purchased new ones as that had been expected. All fitted and working perfectly. Considering the house is now twice the size it was when the original pump was fitted in 2001, the old pump hadn't done bad. If only I had asked the question 18 months ago, I could have saved my ears from the MIL :)

Thanks, once again for your help.

Kev
 
It is set to that, max output, CC3 at 6.5M, by default but you may find that constant pressure CP2 at 4.5M or CC2 at 5.2M will be adequate, its only a few button presses.
 

Reply to Two radiators not getting hot in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
217
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
281
PSxxxxxx
P
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
167
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
441
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
260

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock