Hi all
I have a Vaillant ecotec plus (ground floor) and an unvented cylinder (top floor). This is an s-plan with a downstairs ufh zone and a single 1st and 2nd floor radiator zone each zone controlled by a two port valve. We have had various issues with the installer of this system.
The latest issue is that whenever the ground floor UFH is on or the hot water is on the radiator zone on the 1st and 2nd floor gets hot.
This is being caused by reverse circulation (the return pipes of the rads get hot when the h/w or ufh is on but the red zone is off). The cylinder return is not the last connection before the boiler - the rads and ufh tee in after it.

The installer is returning to run a new pipe back from the boiler to the cylinder upstairs to ensure there cylinder is the last connection before the boiler. I have a couple of questions I would like to ask to ensure the installer does what is required:

1. This boiler requires an ABV and this is installed by the cylinder in the loft. As currently stands this is after the pump and before both the h/w and rad/ufh zone valves. Is this correct?
2. Should the abv be the last connection before the boiler or should the last connection be the cylinder return?
3. Is there any requirement for the returns from the ufh and rad to common together some distance before the cylinder return or is it simply enough that they connect in the correct order regardless of how close to each they do so?
4. Is there a requirement for the return from the ufh and the common return from the rads to connect together in any specific order or again is it just “they must do so before the cylinder return”

Apologies for all the questions but I want to make sure, given other issues we have had which I won’t go into here, that the work that needs to be carried out is done correctly this time.

Thanks for your time, I really appreciate it
 
Last edited:

Reply to Three tee rule and bypass in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
47
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
1
Views
90
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
251
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock