Just about to remove a rad for plaster, but it’s on a UFH manifold.

Having not removed one on a UFH manifold before, wanted to check the process with minds more in the know.
Is the following about right?

• Close off rad circuit actuator/pin with decorating cap, to stop flow.
• Remove rad in normal way

Reattaching rad
• Close off all UFH circuits
• Reattach radiator
• Attach hose and refill rad circuit, removing all air through manifold drain off.
• Detach hose and open all circuits
• attach pressure tester (need to find a wet pressure tester.. been scouring eBay)
• Re-pressure manifold to original bar

That the general gist?
Manifold has AAV on both flow and return.


thanks in advance
 
Cant you just isolate the radiator valves, drain what little volume of water is in the rad and do it that way rather than having to refill whole system and having airlock issues?
 
Cant you just isolate the radiator valves, drain what little volume of water is in the rad and do it that way rather than having to refill whole system and having airlock issues?
I can. I don’t need to drain the whole system (as far as my understanding goes) I will just need to refill the radiator under-floor heating circuit, and will need to re-pressurise the system.
Having not done it before, I just wanted to check so I am 100% what will happen after my reattach the radiator
 

Reply to Temporary Radiator removal on UFH circuit in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, we had UFH installed dowstairs in our house recently, and I'm not 100% sure that it's connected correctly. I'd be grateful if someone could...
Replies
7
Views
1K
Hi Everyone I wasn’t sure whether to post this in here or UFH but hopefully I’m posting this in the correct group. I’m in the throes of a full...
Replies
7
Views
792
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators...
Replies
61
Views
5K
Hi all, I have recently had a UFH circuit added to my existing CH/HW system and had a question on performance when UFH and CH are operating at...
Replies
3
Views
1K
The system is open vented with a Glowworm boiler. It has an LCD controller on the wall - see pic. I just want to remove one radiator for cleaning...
Replies
5
Views
657
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock