Here it is, from the BS 6891:

8.9 Pipes in walls

8.9.1 Pipe runs
Installation pipe shall, where possible, be vertical and shall be placed in ducts with convenient access points or placed in pipe chases.
The installation pipe shall be secured and have as few joints as practicable.

COMMENTARY AND RECOMMENDATIONS ON 8.9.1
Typical methods of installing pipes in walls are shown in Figure 6.

8.9.2 Cavity walls
Installation pipes shall not be placed within the cavities of cavity walls. Every pipe passing through a cavity wall shall take the shortest practicable route and shall be sleeved (see 8.10).

8.9.3 Dry lined walls

Installation pipes installed behind dry lining shall be suitably encased by building material.

COMMENTARY AND RECOMMENDATIONS ON 8.9.3
For typical examples see Figure 6b) and Figure 6c).
 
The diagrams referred to in 6871 only show vertical pipe runs. No mention of horizontal.
Corgi book says horizontal pipe runs should be avoided.
 
"where possible". Site plumbers usually on price so "which is the quickest".
 
You don't run them horizontally if it can be avoided but if it can't be avoided then you run them horizontally :smile:
 
One of those stupid "engineer on sites call" isn't it. Ambiguous at best. Ugh
 
Lets summarise: Perfectly simple, Only run pipes vertical. There is no excuse for making life easy or getting it done cheaper, but some circumstance's horizontal partial runs may be unavoidable.
 
Status
Not open for further replies.

Reply to Running a gas pipe HORIZONTALLY in a dot and dab wall in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
781
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my plumber is coming...
Replies
12
Views
3K
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
327
We have an old gas pipe in the understairs cupboard. The previous occupants had the gas meter moved, but this old pipe remained. This pipe goes...
Replies
7
Views
601
I just had a quote for a new boiler install as follows I dont undertand why a 15-60 boiler pump is needed and a 25-100 pump is needed as well I...
Replies
3
Views
580
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock