Does this have a trv ?
Discuss Reliability of fault codes potterton in the Central Heating Forum area at PlumbersForums.net
Yep, it has a TRV to the bottom left of the manifold, it's hidden away a bit. I've circled it in this photo.Does this have a trv ?
Yep, it has a TRV to the bottom left of the manifold, it's hidden away a bit. I've circled it in this photo.
Why? Is that significant?
Thanks
Isn't the item circled on top of the manifold a thermostatic air vent?.
I assume that is a TMV to give the required much lower UFH temperatures required.
If one of the actual boiler trips is the deltaT between the flow & return then most trip at a deltaT of 30C so perhaps this is what is tripping the boiler but this would/should only happen if no ABV is fitted, you have which we assume is working OK, you can see the effect of by pass vs no pass in the attachments if my calcs are correct.
I think the first thing to establish is what actually are the conditions that flag this low flow circ trip, there is no explanation in your manual and mine might be completely wrong.
I am just assuming UFH requirements but the relative flows and temps should still be correct.
I see the UFH TMV is on the left of the manifold but havn't a clue what you mean by a TRV on the manifold (circled).
View attachment 63686
View attachment 63687
No sorry on the rad that the grey hep supplies can you remove it to test something eg the trv head
Yes, the deltaT is the difference between the flow/return and ideally should be kept ~ 15/20C but with UFH only on because of the ratio of boiler flow to UFH flow then you can have a huge boiler deltaT depending on the boiler flow temp and the UFH (mixed) flow temperatures which means that you can have a very high undesirable boiler deltaT which on some boilers will initiate a trip if it exceeds 30C or so, I only used the attachments to show how the deltaT can change with/without by pass.Wow John!! Thanks for doing those calculations and drawing that out. I'm embarrassed to say that I'm struggling to interpret the findings of them. Am I correct in thinking the "DeltaT" is the difference in temperature between the flow and return? And, if I have an automatic bypass fitted then I need to maintain a difference of 15 deg between the flow and return or the boiler will trip? However, if I don't have an automatic bypass fitted (which I don't now as far as I'm aware) then I can have a difference of 30 degrees between the flow and return?
So, if I'm correct above, I'm better to not have a bypass? Is that correct?
Thank you again for your hard work on this. I'll answer other questions/support in another reply on here.
Yes, the deltaT is the difference between the flow/return and ideally should be kept ~ 15/20C but with UFH only on because of the ratio of boiler flow to UFH flow then you can have a huge boiler deltaT depending on the boiler flow temp and the UFH (mixed) flow temperatures which means that you can have a very high undesirable boiler deltaT which on some boilers will initiate a rip if it exceeds 30C or so, I only used the attachments to show how the deltaT can change with/without by pass.
You have a bypass which is set very low IMO, phot 7 post#12, see posts #15&16 as well.
I find it a bit strange that the systems work fine when running separately but not with both on together.
Can you say how long it takes the boiler to trip if you have, say, the Rads on and you then call in the UFH, does it trip immediately or is there a time delay or whatever.