Should have seen the link to the tower separator, if clean then there should be, theoretically, no pump over at that vent/feed distance of only 50MM, of course it is also a perfect dirt trap but unfortunately cannot be cleaned out easily as there are no compression fittings, if mine, I would consider removing it altogether and just have the vent....cold feed.....pump, or else replace it with a new one if old one cannot be cleaned out.
I would suggest there is definitely a partial blockage there as the pump over only happens with a high flowrate which means a higher pipe velocity and leads to venting.
Re pump readings, LPM = M3/hrX16.666 or if you prefer LPM = l/secX60.
My pump curves are meaningless now as you have a 5M pump (not a 6M) and the settings are a bit confusing, especially the constant pressure CP ones, your attachment seem to indicate that CPi is 0.8M, CPii is 2M and CPiii is 4M, can you just confirm that on your pump that setting CPii is flashing 3.8M on startup? because if its only 2M then there is a big problem with blockage(s).
I would suggest there is definitely a partial blockage there as the pump over only happens with a high flowrate which means a higher pipe velocity and leads to venting.
Re pump readings, LPM = M3/hrX16.666 or if you prefer LPM = l/secX60.
My pump curves are meaningless now as you have a 5M pump (not a 6M) and the settings are a bit confusing, especially the constant pressure CP ones, your attachment seem to indicate that CPi is 0.8M, CPii is 2M and CPiii is 4M, can you just confirm that on your pump that setting CPii is flashing 3.8M on startup? because if its only 2M then there is a big problem with blockage(s).