Discuss Pipework advice - Central Heating System in the DIY Plumbing Forum area at PlumbersForums.net

Messages
58
I have a 320 sqft double storey house with 6 bedrooms. The house is serviced by two heat only boilers (non condensing); a 120k btu (35kw) and a 70k btu (20kw). Both Boilers are installed at ground floor (120k at front and 70k at the back). Front boiler serving front downstairs and upstairs rooms and the back one serving ground floor and upstairs rooms at the back. 22mm Copper pipework from boiler with branches going upstairs and terminated to radiators 8mm. The house has larger rooms at the front side and smaller rooms at the back.

I must tell you that this was installed without heat loss calculation so the front boiler is only serving;

Ground Floor= a 252 sqft room; 320 sqft. Lounge with 600x1400mm Type 11 radiators installed in each room. Both rooms maintain temperature very well.

Upper floor 252sq.ft room (Type 22 radiator recently installed) and a 650sqft lounge with fan assisted coil unit installed.

What I am trying to achieve

I am on my learning curve with the system and my heat calculation tells me that the front 35kw boiler would be enough with 12 radiators in total for the whole house including small radiators in bathrooms. To do this I need to extend the pipework from front to back; two copper pipes 22mm for 35ft length.

Questions :

1. From where do I take a connection out from existing 22mm copper pipes; upstairs or downstairs? Would this length require a separate pump to be installed to serve pipework this long?

2. Would the existing heating be compromised (front rooms if I extend the pipework)?

3. Would I be saving any money; running two boilers instead of one. I have gas rated the boiler and bigger boiler consumes 1m3/hr at 70deg C flow. Extending the pipework will increase my gas usage, correct?

Many Thanks in advance.
 
1. Difficult to say without seeing the layout but I suspect the most convenient option would be the way to go with a correctly sized pump.

2. Shouldn't be if system design is correct.

3. If the boiler has been correctly sized the only reason to run two boilers is for redundancy and if you'd prefer say independent hot water provision.
 
Maybe this time it's best to get a decent engineer in, to do it right!?
In my area where I live it is difficult to get heating engineers! To make client comfortable and no complaints they just oversize everything here at customer's expense and ignorance, they did this to me when they installed the system and now they want to sell me one of their fancy boilers.
My boiler works well, I only use 3 to 4 bedrooms so I won't be using all 6 bedrooms.
 
3. If the boiler has been correctly sized the only reason to run two boilers is for redundancy and if you'd prefer say independent hot water provision.
We don't use all 6 bedrooms but one of the upstairs bedroom which is in our use is connected with small boiler., with current energy prices it doesn't make much economic sense to run boiler to heat one bedroom. I have the front boiler running constantly so to gain efficiency I was thinking of connecting this bedroom or all 5 radiators (connected to the smaller boiler at the back with the bigger boiler).
For hot water we are using electric geyser since I have 11kw solar panels installed.
 
I have asked two plumbers for quotes; one is saying copper at 20mm and the other is insisting on PEX 20mm. He says that he can lay copper pipe but elbows will restrict the flow of water hence PEX is better? Any advice or suggestions? Thanks in advance.
 
I for one would not use PEX Pipe even if they were given it away Would always use copper but its expensive or failing that 26mm multilayer pipe might be the way to go . one 30KW boiler is more then enough to heat 12 Rads But in order to save yourself money this heating system needs to be Zoned Running two boilers is costing you money The attic or roof space has to be lagged 30% of your heat goes out through Attic. At the very least I would separate up stairs from down stairs including hot water All gas appliances have to have the necessary Gas at any gas boiler to work efficient under size gas to a appliance is what you do not need As regards the extension i would run separate pipe work for these rads Depending on how many rads that are involved again i would also zone this extension All rad circuits controlled by room stats Hot water controlled buy Cylinder stat failing that the combi boiler takes care of the hot water then you can either have the other zones controlled by motorized valves and room stats But if this home has no controls its cycling on the boiler stat which in itself will just rob you this is a given . What you do not want to do is to heat any space that you do not use
 
I for one would not use PEX Pipe even if they were given it away Would always use copper but
Thanks Dave for your thoughts. I am going to use copper 20-22mm depending on cost. My plumber is saying that 15-18mm should do the job but I am insisting on using 20mm to the very least.
By extending the pipework; 2 pipes for flow and return, should be enough to cater for 5 radiators.
Existing boiler has 5 radiators with a total load of 14 kw (~50k btu).
 
55kW sounds a lot for 3200 sq ft (you wrote 320 sq ft, but I'm assuming that's a typo), unless that's 3200 per floor? I'm tempted to agree with your calculation of 35kW.

To put your boilers into context, there's a Victorian house I've worked on which has 13 radiators, and an internal floorspace of 3282 sq ft (total walkable internal area). Cavity wall and loft insulation, but weird shape with a lot of surface area and not especially airtight. Some of the windows are old sliding sashes, but most have internal secondary glazing. It has a 24kW boiler for heating and hot water purposes. The boiler is certainly not undersized. This is in Colchester, so not much colder than London. The boiler is also a heat only with a vented cylinder.
 
55kW sounds a lot for 3200 sq ft (you wrote 320 sq ft, but I'm assuming that's a typo), unless that's 3200 per floor? I'm tempted to agree with your calculation of 35kW.

To put your boilers into context, there's a Victorian house I've worked on which has 13 radiators, and an internal floorspace of 3282 sq ft (total walkable internal area). Cavity wall and loft insulation, but weird shape with a lot of surface area and not especially airtight. Some of the windows are old sliding sashes, but most have internal secondary glazing. It has a 24kW boiler for heating and hot water purposes. The boiler is certainly not undersized. This is in Colchester, so not much colder than London. The boiler is also a heat only with a vented cylinder.
Thanks Ric for your comments. I have attached floor plan with covered area of my property. I apologize for the typo but this is the total area of the property and not the covered area, the covered area for two floors (Ground+First floor) is 4500 sq.ft. with no insulation cavity walls, single glazed aluminium windows. Your example of old victorian house fits perfectly with mine!
I have separate arrangement for hot water so boiler is for heat spacing only. My btu or kw requirement of the property is what I have currently installed in terms of radiator. I had a room upstairs that took ages to warm (see attached layout) so I realized that radiator is not putting up with the heat requirement of the room so I upgraded it with a double panel and it is working perfectly now. I have to tee off a 22mm connecting from flow but I am working which is the best location to tee off; from Upstairs flow line or downstairs line where boiler is installed.
 

Attachments

  • Picture1.png
    Picture1.png
    221.6 KB · Views: 11
  • Picture2.png
    Picture2.png
    325.7 KB · Views: 13

Reply to Pipework advice - Central Heating System in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
282
PSxxxxxx
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
265
Hello I am looking to install a slimline dishwasher (integrated) into a cupboard in my kitchen. The depth of the dishwasher is 550mm and the...
Replies
22
Views
593
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the...
Replies
0
Views
178
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
555

Newest Plumbing Threads

Back
Top