Hi all, Ever since I was an apprentice plumber going back 20 or so years when we installed sealed heating systems - We always made sure that 22mm pipe would go into the expansion vessel ie do away with the actual fittings that come with it which were 15 mm and put our own 22mm female to copper adapters on the vessel.

But I am thinking say for 15kw boilers is this really necessary could i just connect it using 15mm pipe?
Thanks!

ReadingPlumber
 
Look at the connections of the expansion tanks in some of the boilers today.
I saw one today that had a 6mm pipe connected to the expansion tank, but generally they are 10mm pipe.
In old school terms 1/4" & 3/8".
 
Some of the more reputable mfrs, heatline, vokea, biasi, feroli use an braded hose with 6mm internal dia when new! Would think the most important thing was to make sure the EV was of adequate size for your system!
 
Some of the more reputable mfrs, heatline, vokea, biasi, feroli use an braded hose with 6mm internal dia when new! Would think the most important thing was to make sure the EV was of adequate size for your system!

Heatline, Vokera, Biasi, Ferroli.....Reputable?

Are you for real?
 
A touch of sarcasm! Only ever fit valiant, Baxi and ideal. Fix plenty of the reputable ones though. Wb installer but personally wouldn't fit one in a skip after doing repairs in the newer models!
 
baxi are pants, ideal are okish, and vailant steal your customers........... id rather fit a WB. but each to his own.
 
My main issue with wb is the amount of plastic and the ridiculous amount of room they leave you to work inside boiler? Wb rabbit on about ultrasonic welded hex ...... What about flow-turbines, and plastic hydroblocks that pinhole?

Why don't you like Baxi? Cheap and cheerful good service team and loads of room in case, parts are relatively standard? Duotec 1 is a pretty solid boiler along with mega flow? Obviously Bermuda is the daddy of all BB?
 
Status
Not open for further replies.

Reply to Pipe size going into expansion vessel on sealed heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
381
hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn...
Replies
5
Views
707
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
487
losing pressure
L
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
511
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
521
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock