Welder
Thanks Chris. Gosh never knew that.Series 20 & I think 16 are bubbles Dave.
Discuss Oso unvented. Cold water through tundish in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Thanks Chris. Gosh never knew that.Series 20 & I think 16 are bubbles Dave.
Come on Ash there must be something to accommodate expansion, either it is a bubble top or it has a vessel/s ?
If it hasn't got a vessel did you recharge the bubble, it could be that the expansion relief was discharging because the expansion was not being accommodated.
In which case it just needed a service.
If I isolated the inlet but it's the t and p that is faulty would this not continue to run after I have isolated?
Thats because you never asked BBA.Thanks Chris. Gosh never knew that.
Depends. As you remove the pressurisation from the incoming side then, if it's borderline on the pressure side, it may sit back down and seal. You could only tell that if you had pressure gauges all over the show.
Did you reset the bubble? How long did that take?
Not long as the customer had done it themselves twice before I got there trying to sort the issue themselves. They said it's been runni g constantly for about 2weeks.
& it wasn't coming from the T&P ? Then it was the relief that needed replacing. If the composite (combination) valve set is old, >12 years, I might suggest to customer it is replaced but not the T&P. I am generally against carpet bombing parts on jobs I think it is unprofessional but then occasionally I will get court out.I have the customers copy of the manual Has the air gap with the instructions on the side like with the megaflo. Followed that and no change.
TBH, I think you're right. Change the sodding lot and be done with it. You are not going to get paid for being clever & diagnosing in this instance. #Pragmatism.
& it wasn't coming from the T&P ? Then it was the relief that needed replacing. If the composite (combination) valve set is old, >12 years, I might suggest to customer it is replaced but not the T&P. I am generally against carpet bombing parts on jobs I think it is unprofessional but then occasionally I will get court out.
BTW you shouldn't remove customer copy of MI's. Get yourself an iPAD & download them as required would be my tip.
Reply to Oso unvented. Cold water through tundish in the Plumbing Jobs | The Job-board area at PlumbersForums.net