Trevormp

I have an oil fired boiler that is firing up fine, but reaching temperature quickly as it is not heating up the radiators. The pipes in and out are hot. I also have a junction upstairs with feed in pipe and the two pipes leading off are also both hot (one to HW tank and the other to the radiators). I have bled the radiators, there was a lot of air in two radiators but now sorted, but heat is still not reaching the radiators - any of them! The pump seems fine as it is vibrating. Can you suggest a solution (advices would be appreciated as my wife is not impressed with my efforts so far!)
Thanks
 
it sounds like you have a 3 way valve(the 'junction' you describe)This valve opens to allow water to flow to HW,to Heating,or to both.It has a lever on the head that you can manually open,if you do this and the radiators get hot,then the head is probably faulty.

The pump could be the problem also.Is the hot water working?

Try to open the manual lever on the 3 way valve and see if that works first.
 
Many thanks for your reply Bartdude.

I do have a Honeywell V4073A1039 3 way valve. but i cannot see a lever on it - can you tell me where it is situated? The hot water is working fine, so it sounds like it could well be the valve.

Further advice will be much appreciated.

it sounds like you have a 3 way valve(the 'junction' you describe)This valve opens to allow water to flow to HW,to Heating,or to both.It has a lever on the head that you can manually open,if you do this and the radiators get hot,then the head is probably faulty.

The pump could be the problem also.Is the hot water working?

Try to open the manual lever on the 3 way valve and see if that works first.
 
images-23.jpgThe lever is situated on the side of the silver box on the valve head.You can see it in the picture below the black cable.

You need to push the lever sideways,there should be resistance.Push it as far as it will go,you then need to hold it up to engage it into a slot to hold it in place. If your heating then works the valve head needs to be replaced. The head only can be replaced,there's no need to drain the water system. It's a job for an engineer though.
 
Last edited by a moderator:
View attachment 1782The lever is situated on the side of the silver box on the valve head.You can see it in the picture below the black cable.

You need to push the lever sideways,there should be resistance.Push it as far as it will go,you then need to hold it up to engage it into a slot to hold it in place. If your heating then works the valve head needs to be replaced. The head only can be replaced,there's no need to drain the water system. It's a job for an engineer though.


Many thanks, Bartdude. My valve is fitted vertically and the lever is on the underside so had not seen it until now. Have just tried your suggestion and that seems to be the problem, so will get head replaced. Once again thanks for your help - much appreciated.
 
Status
Not open for further replies.

Reply to Oil fired boiler not getting heat to any radiator with Honeywell V4073A1039 3 way valve in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
170
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
263
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
375
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
268
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock