Might be a design fault where the water is being sucked out of a trap somewhere,
Block overflow and put plug in one item at a time to try and isolate which it may be.
We think its coming from the kitchen sink, we did as you suggested and when unplugged kitchen sink the smell came back but its intermittent but its disgusting smell. We now have heard through the grapevine that the builder intends to put a vent onto holding tank next door. Apparently it was suggested by the Building control inspector (agent from the local council) that this may be the problem. What do you think? Any suggestion will be welcome, its really getting us down!
 
We have just heard through the grapevine that the builder intends to 'vent' the pump station tank. Do you think that is the problem?
It's possible that an open vent will help. Building regs say that a foul drainage system should have an open vent to atmosphere (as in soil stack) somewhere to relieve positive pressure.

AAV's only deal with allowing air into the system to avoid water in traps being sucked out. They don't help in the event of a higher pressure in the drain system (possibly created by the pumping station) that could push foul air through a shallow trap.
 
Not really what they are designed for but would solve your problem short term if this is getting you down ?? Kop
 

Attachments

  • Screenshot_20210717-183150.png
    Screenshot_20210717-183150.png
    794.1 KB · Views: 16
  • Screenshot_20210717-183208.png
    Screenshot_20210717-183208.png
    869.7 KB · Views: 17

Reply to New build house smell in the USA area at PlumbersForums.net

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock