How is your system performing since change?.
Still not great really, pump speed 1 means the boiler is cutting out regularly due to temp difference between in and out, also the rads on cold days don't seem to get up to temperature quickly or stay there. I have also had a few instances once everything has gone off of a water surge up the vent into the header tank and out through the overflow into the garden.
So I have run a Sentinel x800 through the system over the weekend and today I am going to disassemble what I can around the vent and cold feed area, replace the 3 port valve (I bought a non honeywell version so we will see how that goes) and see if I can see anything new.
Will report back later today.
[automerge]1574086754[/automerge]
New 3 way valve fitted. Most of the pipe work boiler side of the pump was blocked by about 50% including the tee for the vent, the blockage didn't go much further south than this and was also clear either side of the Y valve. Pump inlet and outlet around 30% also blocked with black residue.
Took it all apart (compression fittings only) cleaned out the pump and pipework as best as I could and refitted. After several hours of bleeding the system is 'relatively' happy, in that there is no longer any water coming out of the vent, regardless of CH/HW selection or pump speed.
There are still problems however, one of my rads (bathroom) I cannot get hot for love nor money, throttling back all other rads just creates too much of a restriction somewhere and the boiler has a hissy fit and shuts down in seconds. All other rads are getting hot fine. So there must still be an airlock somewhere, or another restriction/blockage in the CH pipework restricting flow. Or my boiler settings are just plain wrong for my house.......
Same happens if I select pump speed 1 and all rads are throttled normally, boiler heats up too quick and shuts down.
One step forwards - 2 steps back!