- Messages
- 312
Any idea what the valve I have arrowed, which looks as though it could be partially tured on, is for?
Just curious....
Just curious....
Discuss High gas usage for boiler. in the USA Plumbers Advice area at PlumbersForums.net
Sure.it’s to drain the system apparently? Runs off outside?Any idea what the valve I have arrowed, which looks as though it could be partially tured on, is for?
Just curious....
Just to add to the confirmation - here is yesterdays usage.That's why I posted this again, its pretty obvious that DHW usage couldn't account for the difference and as I said IF CH can reasonably be ruled out then ???. If one assumed DHW @ 200 litres/day at 60C = 12kwh so 31kwh unaccounted for. I still have a suspicion that the boiler was enabled and firing on its own stat which wouldn't take long to dissipate that 31kwh especially if that ABV was/is passing.
Thanks John. Yes yesterday was ok when the heating was not onThat seems OK, elect use of 14.11Kwh & gas usage, (5.61x11.33), 63Kwh. I used 82kwh yesterday for CH+DHW. So everything seems fine? and the big problem was (last) summer usage?? You will just have to keep monitoring usage IMO, you have a excellent reporting system, just use gas meter to verify same.
Your bill below, for last summer gives 11.33kwh/M3 so used that, above.
Last summer you used a average of 43.36Kwh/day, for 29 days, apparently for DHW only, that equates to 775 LPD of hot water at 60C or 1328 LPD at 40C, enough to wash a small army?.
Heating was not on yesterday, wasn't on the ball there as I thought you went out at 9PM, so you used apparently 63Kwh on DHW, assuming mains at 6C, = 1,003 litres of water at 60C. The DHW heating was enabled from 11 to 1, 2 hours?? so the coil had to be inputting 31.5kwh/hr or a 31.5kw coil, no way. If you assume say 10kwh max was used for DHY heating then, 63-10, 53Kwh unaccounted for, if you take yesterdays usage, of 15.68M3, 178Kwh and subtract 53Kwh you end up with 125Kwh which then isn't outrageous of if no HW heating then consumption, 178-63, 115Kwh, normal enough for your sized house + DHW needs??.
IF no body pinching gas and IF no meter problems then it goes back to the boiler firing, you were averaging ~ 0.3M3/hr, 3.4kw which you easily be dissipated in the piping with all zone valves closed.
I thought you said you were going to run on the cylinder immersion for a few days with the heating coil didabled?. If/when you next go out then monitor the energy usage.
Yes, didn,t realize heating was on earlier and the cylinder consumption of ~ 11.5kwh seems spot on to heat ~ 200 litres of water. So yesterdays CH consumption was ~ 178-11.5, 167Kwh, suppose seems a bit on the high side but you are heating a lot of house for long periods each day. You were averaging ~ 8 to 10 kw boiler output.
Ok - if that’s in the realms of possibility I guess I can accept that.Yes, didn,t realize heating was on earlier and the cylinder consumption of ~ 11.5kwh seems spot on to heat ~ 200 litres of water. So yesterdays CH consumption was ~ 178-11.5, 167Kwh, suppose seems a bit on the high side but you are heating a lot of house for long periods each day. You were averaging ~ 8 to 10 kw boiler output.
Very valid point! It could well be!!! And I’ve no real way to prove it now!Just throwing this out there. What if the old meter was under reading and you have actually been using this amount of gas per year. New meter gets installed 2 years ago, reads correctly and now you notice it.
From reading the thread, everything pretty much checks out. Nothing posted stands out as odd for a property like yours. Perhaps if I saw the property it would, who knows.Very valid point! It could well be!!! And I’ve no real way to prove it now!
Your synopsis seems sound.From reading the thread, everything pretty much checks out. Nothing posted stands out as odd for a property like yours. Perhaps if I saw the property it would, who knows.
From the basics, you check the gas line for tightness. No leaks confirmed. Good.
You check the boiler consumption/meter readings, yup it’s using the correct amount of gas. Good.
This means gas is only being used to generate heat via combustion.
This heat has to go somewhere.
No leaks on the cylinder wasting hot water. Good.
House not too warm. Good.
Not really anywhere else an increase of 5 times previous could come from.
I agree.Your synopsis seems sound.
I’ve spoke to a thermal imaging and heat efficiency company who really new their stuff and pretty much said their same. They do thermal scans and air tightness test to see where the heat is escaping and advise on the remedial work we could look at - so I’m seriously considering it to at least get some closure!
so please explain why a 24kw boiler is good for a number of rads?I think your Worcester bosch junior 24i system boiler is not getting the proper gas supply that's why your boiler not working properly. The heating output is 24Kw is ideal for any property with around 15 radiators.
Please share the pics so that I can help you more efficiently. If your boiler comes under the brand warranty then please contact customer care.
The second option will be you can take advice from the professional rooter and plumbing service provider near your area. Because the boiler system needs an engineer to fix it.
No offence taken! I think your right and The survey will just be to put a final confirmation on it!I agree.
This isn’t a dig, just my experience. Customers always talk about what can they do to save money on gas, can we upgrade to smart controls, upgrade the boiler etc.
Once you take into account the cost of these items, they really don’t save a huge amount. I’m not saying don’t do them, but they are not the golden gun.
A property takes a certain amount of heat energy to keep it at a certain temperature. Today’s high efficiency boilers running efficiency in the 90%+, don’t have a lot of room to improve.
With that and the age of our housing stock (subpar thermal insulation), the best efficiency increase is to stop that heat from escaping the property.
@stevedurban: What was the conclusion of your high gas usage. Did you get the survey done for heatloss from the property?No offence taken! I think your right and The survey will just be to put a final confirmation on it!
Reply to High gas usage for boiler. in the USA Plumbers Advice area at PlumbersForums.net