31kw can go about 15m equivilant in 22mm, so the pipe size is just about ok.Appologise for wrong pipe sizing, equivilant Length is 15.3 meters with all fittings taken into account and actual pipe run of 8.1 meters if this makes a difference. Thanks for all your help.
Thanks for the reply, i was not aware of the pressure loss through the gas valve. If this is an issue then why don't all manufacturers include a test point at the isolation valve?31kw can go about 15m equivilant in 22mm, so the pipe size is just about ok.
I’d bet the engineer just added 1.5mb to the 15.5mb reading due to the pressure loss through the gas valve.
Some do/some don’t. Guess it all comes down to cost.Thanks for the reply, i was not aware of the pressure loss through the gas valve. If this is an issue then why don't all manufacturers include a test point at the isolation valve?