Hello all,

I currently have a gravity hot water system - with a 110x60x60cm water tank and a small one (expansion vessel?) in the loft, the water pressure in the bathrooms (3 on first floor) are very poor, especially the master bedroom en-suite (the furthest way from the cold water tank) which is unusable for shower. My understanding is that the cold water tank is feeding both the hot water cylinder and the cold water taps in all bathrooms. And I have tested at the ground floor tap, the mains water is 22L/mins so not so bad at all.

I also had a look in the loft and find out the cold water tank is the old style open tank with plastic sheet covers on top, which already fall off into the tank so the tank is quite dirty and I can see the built up limescale at the bottom.

So apart from the shower pressure I have the concerns about the water quality.

My understanding is that I have two options:

1. Keep the existing system with the loft cold water tank. Add multiple small pumps for each bathroom, and change the cold water tank to poly water tank with lid. This system is the safest system as the tank and cylinder is not pressurized, but the water quality could be getting worse along the time when the limescale built up and dust etc get into the tank.

For this setup my main concerns are Water quality over time and pump noise. Do people just get the tank professionally cleaned regularly? Or can I by pass the cold water tank and split the mains water (currently feeding the cold water tank) then connect all bathroom cold water pipes to it, so my bathroom cold water taps are feed directly by mains water - fresh and at the mains pressure. Then adding pumps for each bathrooms' hot water to balance off the pressure.

2. Convert to unvented cylinder, so the cold water will be at mains supply pressure. With 22L/min flow rate tested at ground level tap, am I guaranteed to have good shower performance in all bathrooms ( assuming only one in use or 2 showers simultaneously). And we are also slightly worried about the safety of the cylinder as it may blow up if not fitted right - I was not aware it could explode and cause serious damage, the cylinder fitting guy came for a quote and asked me to check out the explosion video - he was trying to make a selling point as he's manufacture approved installer and I am seriously put off by the possibility of it exploding.

The current cylinder is in the cupboard next to my daughter's room so my wife asked me to move the unvented cylinder to the garage if we went with the unvented, but then my double garage would become single as I cant park two cars anymore with the cylinder installed there...

Considering I will be living in this house for a long time so the cost does not play much here, only looking to the best option for the long run.

Thanks a lot for any advice in advance.
 
If I were you I think I would go for the unvented option.
You need a good, G3 compliant Heating Engineer to come and advise you first, without filling you with fear.
These systems have been around for many many years and are used in a variety of situations.
If installed and maintained correctly, they are just as safe as anything else.

If you have gravity hot water ( presuming you mean what I think you mean ) you will need advice on the boiler/system side too, as it will need to be upgraded.

I hope this helps.
 
I would go for an unvented system also. That is the only way to get anywhere near the flow rate you have at the minute. It would also mean you could run more than 1 bath/shower at a time with no hassle of losing pressure. The initial cost of the install/setup of the system may put some people off, but in my opinion the long term benefits out weigh this cost.
 
If I were you I think I would go for the unvented option.
You need a good, G3 compliant Heating Engineer to come and advise you first, without filling you with fear.
These systems have been around for many many years and are used in a variety of situations.
If installed and maintained correctly, they are just as safe as anything else.

If you have gravity hot water ( presuming you mean what I think you mean ) you will need advice on the boiler/system side too, as it will need to be upgraded.

I hope this helps.

Thank you. I had a manufacture approved installer came for a quote and he said I can replace the cylinder for now and boiler at later time if I wanted, should I have someone else come for a second opinion on whether my boiler would cope with the new cylinder?

So if all things done right (good quality cylinder, manufacture approved installer etc), I should not worry install the unvented cylinder between the bedrooms on first floor? or would it worth the hassle to move it to the loft or garage just for the extra peace of mind...
 
you can locate the unvented cylinder in the loft or garage yes, you can even get horizontal cylinders designed for lofts.. your installer will be able to advise you on this regarding the cold feed and the cylinder location.
 
Thank you. I had a manufacture approved installer came for a quote and he said I can replace the cylinder for now and boiler at later time if I wanted, should I have someone else come for a second opinion on whether my boiler would cope with the new cylinder?

So if all things done right (good quality cylinder, manufacture approved installer etc), I should not worry install the unvented cylinder between the bedrooms on first floor? or would it worth the hassle to move it to the loft or garage just for the extra peace of mind...

As above.
Have no fear form the unvented Cylinder !
Trust me, I'm a Plumber.
 
Thanks all, I've done some more research and with the feedback here I think I'll go with unvented cylinders. now will look into costs and installers etc.
 
Have a look at the dual coil type. They're not that much more expensive and it would give you options for a later date, such as adding solar.
 
There's a lot of scaremongering about risks with unvented systems but the reality is there isn't a problem if things are done right. Taking an example, if you're running the unvented cylinder off your heating boiler the only way you could have an explosion would be for all the fail-safe devices on the boiler to fail, the heating system somehow to get the cylinder above 100C, all the safety devices on the cylinder to fail as well as the pressure exceeding the rating for the cylinder etc. etc. You see what I mean! Can't say it MIGHT NOT happen, but the chances are 1 in 10-to-the-power-of-my-overdraft!
And for those who say a vented cylinder is safer, the only cylinder I've seen explode was a 600 gallon vented one: some yobs torched the chemistry lab in a local secondary school where the hot water pipes ran through the ceiling. Water flashed to steam, blew back to the boiler room next door, blew the bottom out of the cylinder which leapt 3ft into the air hitting a 5" gas main. Fire brigade turned up to find a fire, chemicals, flooding and a gas leak! Fun for everybody :p
 
Status
Not open for further replies.

Reply to Gravity hot water system - replace or improvement ideas please advise in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
218
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
441
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
217
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
281
PSxxxxxx
P
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
392

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock