if i was to remove a gas fire and cap off the supply using a black iron cap, would i be able to use leave the branch with the cap on under the floorboards? assuming it was adequately supported. or would i have to completely remove the branch or leave the cap accessible to purge from.
 
Ideally completely remove the branch if no longer required.
If capping off under floorboards this would be classed as an inaccessible area and would require a soldered end cap.
 
I was told it was ok where I used to work but I used to just solder a cap end on instead. For the sake of an extra ten minutes its seems worth it to me. I'd do it just because it made me feel better about the job and its your name going on the ticket not your bosses or gas safes.
 
What,one of these?

images-20.jpg

Or does he mean compression?
 
An iron cap is allowed under floor boards, compression caps arent.
 
solder to back iron wtf. obviously onto the black iron to copper adaptor used for restricter elbows. the one in the picture threaded. why is it ok for threaded but not compression?
 
This is another one of the not so clear rules/regs.
BS6891 specifically mentions compression joint and union joints must be in accessible areas to allow for tightening the joint to make gas tight. It does not specifically say threaded fitting cannot be used.
But, does a threaded fitting not need to be tightened to make gas tight?

I was taught that mechanical fittings cannot be used in inaccessible areas and that is what I have stuck by. I suppose it is open to interpretation, but I do not see how you can allow a screwed fitting but not compression.

As far as I am concerned the safe option is a soldered cap.

Maybe the reason it does not specifically say threaded fittings cannot be used is due to the Malleable Iron installs, but that is a different entity carried out under a different set of standards.
 
why is it ok for threaded but not compression?

A compression fitting and a screwed iron fitting are 2 totally different jointing methods.
The compression depends on the ring being compressed to hold it. Lateral movement will distort it with the chance of it leaking.
A screwed fitting grips by its threads and once tightened any lateral movement will have little effect. The joint is a lot stronger than a soldered one.

If MI pipe had to be accessible there would be no way to run pipes in many non domestic. Welding is not a viable option on smaller pipes.
You can use iron on domestic pipework too, anywhere you like. Hardly anyone does as it would take most longer to fit they would most likely not have the tools to do it.
 
This is another one of the not so clear rules/regs.
BS6891 specifically mentions compression joint and union joints must be in accessible areas to allow for tightening the joint to make gas tight. It does not specifically say threaded fitting cannot be used.
But, does a threaded fitting not need to be tightened to make gas tight?

I was taught that mechanical fittings cannot be used in inaccessible areas and that is what I have stuck by. I suppose it is open to interpretation, but I do not see how you can allow a screwed fitting but not compression.

As far as I am concerned the safe option is a soldered cap.

Maybe the reason it does not specifically say threaded fittings cannot be used is due to the Malleable Iron installs, but that is a different entity carried out under a different set of standards.

The BS6891 does not allow compression fittings in inaccessible area's. Black Iron pipe and fittings are OK, infact there better than copper.
 
screwed caps are acceptable even if its on to a brass thread its compresion thats not allowed and definatly no pushfit
 
I thought he may be talking about using a 1/4" male iron plug screwed into the fire restrictor elbow above the floor. This would be correct with the correct PTFE of course....
 
Status
Not open for further replies.

Reply to gas fire removal in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
252
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
234
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new...
Replies
1
Views
249
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
227
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
540
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock