F

fantata1

In these warm summer months we switch off the heating circuit but leave the hot water circuit on the timer. This summer the radiators are still getting warm when the water is on.

I did the troubleshooting and have found that the two port valve on the heating is not closing fully on the actuator. The actuator is moving the valve, but I have found that when I take the actuator off I can manually close the valve another 1/4 turn and that fixes the problem (the pump also sounds different so know the flow is changing too). The valve is moving freely so isn't sludged up.

The valves are [FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]BGMVSP-2 which I assume are rebranded Drayton ones. Would a new actuator head fix this or should I go ahead and change the whole valve? Note I have already bought a Honeywell to replace the valve but thinking about it would prefer a quick fix without draining the system (being lazy!)
[/FONT]
Any help or advice is appreciated.
 
Change the body and head mate. You'll kick yourself if you don't. Hardly anything in the price difference.
 
I've never had an issue by just changing the heads. I must of been lucky.
 
well sometimes you find a body that don't mind taking head,other times just not interested.......

:eek:
 
Change the body and head mate. You'll kick yourself if you don't. Hardly anything in the price difference.

i agree with adam+1,false economy not too ,i have found sometimes that a sticking spindle causes the motor to burn out in the first place ,plus they can burst through the spindle
 
Thanks all. I guess I need to stop being lazy and spend a couple of hours changing the complete valve. Job done right and all........
 
Thanks all. I guess I need to stop being lazy and spend a couple of hours changing the complete valve. Job done right and all........

No short-cut advice given on this forum....

Laziness and half hearted attempts are not acceptable practices condoned by this forum

* unless you have access to the Plumbers Arms - where all short-cut advice is given freely with guarantees.
 
Last edited:
Cheapest option would be get the paddle/service kit & possibly replace the motor mate
 
Status
Not open for further replies.

Reply to Faulty valve actuator? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi I have a 4 zone / 7 loop UFH system. 2 zones (4 loops) always get hot when the system is on when the zone thermostats and actuators are...
Replies
14
Views
1K
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
309
Hi I have a fully pumped heating system fitted with a Drayton MA1 diverter, after the summer run the heating stopped coming on, so I replaced the...
Replies
3
Views
625
M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently...
Replies
1
Views
426
Hi folks, hoping someone can help with a problem that's been perplexing me since just before Christmas..... I have a wet underfloor heating system...
Replies
19
Views
1K

Newest Plumbing Threads

Back
Top