Discuss Faulty heat exchanger in the Central Heating Forum area at PlumbersForums.net

Messages
7
Hi,

Boiler is losing pressure, from 1.5 bar to 0 bar in about 4 hours.

Have checked all rads and seem to be fine, no water out external prv pipe.

If the heat exchanger is faulty what do I need to look for?
There is a constant run of water from the condensate pipe when heating on but not sure if this is normal or the amount it should be. Reading other posts seem to suggest if in condensate points to a heat exchanger issue. I have attached video of anyone could advise if this amount of water is normal when heating on
 

Attachments

  • IMG_1279.mov
    46.2 MB
Easiest way to check is to isolate boiler by closing off the F & R valves.
Close heating water inlet at this time also
Leave the boiler under pressure and see if the pressure drops.

Don't operate the boiler during this time
 

Reply to Faulty heat exchanger in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
390
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
254
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
440
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
313
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock