C

CNelson

I have an unvented system in my home. The fitters that installed it recently came back to replace the expansion vessel as it kept hissing. They said it was a fault with the seal on the expansion vessel. Unfortunately, the new expansion vessel is still hissing.


It sound like boiled water hitting a cold surface, with some gurgling sounds. But predominantly hissing.


When I put the heating thermostat up high for any length of time then switch it off, that's when the hissing happens.


The tundish is dry.


However, the pipe from the expansion vessel to the tundish feels hot.


Can anyone advise about this problem?


Thanks very much.


-CP
 
I assume you checked they were g3/unvented qualified?

There's nothing you can do on this.

Check that they do have g3 and get them back. If they don't then demand someone who is as they are placing your lives in jeopardy.
 
Here's a picture. The expansion vessel is a zilmet.

IMG_5107.JPG
 
I don't think you could distinguish anyone particular noise in that area, there are so many elbows and the pump is so near there will be lots of noise that sounds like a snake, the whole plumbing job is a complete mess, pump impossible to get at , electrics hanging lose on a board, wish you hadn't sent the photo now, there is just one item there that makes me shudder, two 15 mm couplings(sockets) within 6" of each other, what has the world come to!!! Its been throw in, the plumber needs to go to Specsavers, sorry I can't help it, it's a very low standard. I can't see any pressure gauge for charging???
 
Last edited by a moderator:
I don't think you could distinguish anyone particular noise in that area, there are so many elbows and the pump is so near there will be lots of noise that sounds like a snake, the whole plumbing job is a complete mess, pump impossible to get at , electrics hanging lose on a board, wish you hadn't sent the photo now, there is just one item there that makes me shudder, two 15 mm couplings(sockets) within 6" of each other, what has the world come to!!! Its been throw in, the plumber needs to go to Specsavers, sorry I can't help it, it's a very low standard. I can't see any pressure gauge for charging???

I can see the guage. Its connected to the prv below the exp vessel.

Looking at the pic its probably the air release valve
 
Its a bubble top so problem is with the red vessel on the sealed heating system, get them back to set the the vessel charge to that of the static head pressure / cold fill.

P.S. Two couplings on a 15mm safety valve discharge, the end of the world is here !!!
 
So that's the expansion vessel for the heating system then?
Probably the Air eliminator as said before :)
 
Status
Not open for further replies.

Reply to Expansion vessel on unvented system is hissing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock