Hi folks, just a regular member of the public here, learning all he can before having a new combi-boiler and radiators installed in my old victorian flat. For years I've just had some fan heaters! But now it's time to upgrade.

I'm fairly techie, but I can't see why your would range-rate a boiler, if it modulates anyway. I've read and watched as much as I can; but the answer eludes me. I'm most likely misunderstand something, so would be so grateful for your help.

Thanks! :)
 
It is worth fitting the external temperature (weather) compensation sensor to the Vokera - it is a simple plug in connection. That then adjusts the boiler water temperature ( heating only not hot water) according to the outside temperature
 
The vision 20S restricts the output to 75% for 15 minutes on each start up so a automatic measure of output, desirable to you or not.
You want to check this out on your combi model because you certainly require full output for your shower.

"With the selector switch in the heating & hot water position and any additional controls (time clock, programmer, room thermostat, etc.) calling for heat, the appliance will operate in the heating mode. The pump and fan will be activated via the flow temperature sensor. When the fan is sensed to be operating correctly (tacho signal), the ignition sequence commences. Ignition is sensed by the electronic circuit to ensure flame stability at the burner. Once successful ignition has been achieved, the electronic circuitry increases the gas rate to 75% for a period of 15 minutes "

Just checked out your model, as I thought it doesn't limit the output to 75% on HW but does on CH (on each start up) for 15 minutes so you will have to put up with that on a cold morning.
 
Just checked out your model, as I thought it doesn't limit the output to 75% on HW but does on CH (on each start up) for 15 minutes so you will have to put up with that on a cold morning.

Many thanks! So interesting. Could you be so kind to explain (like you're talking to a 5 year old 👶🍼) why the boiler does that? What is it aiming to achieve?
 
That would be quite a good question from a 5 year old, the short answer is that I don't know, I was a bit surprised when I read that re my relation's Vokera 20S. Technically, I can maybe see a reason for it being limited for a minute or two because it fires up at approx that output, but not for 15 minutes, I would suggest that your installer speak to Vokera as its possible that they will instruct him on how to override this except that there is something specific to these boilers.
 
That would be quite a good question from a 5 year old, the short answer is that I don't know, I was a bit surprised when I read that re my relation's Vokera 20S. Technically, I can maybe see a reason for it being limited for a minute or two because it fires up at approx that output, but not for 15 minutes, I would suggest that your installer speak to Vokera as its possible that they will instruct him on how to override this except that there is something specific to these boilers.

Thank you for that advice, I will have my installer speak to them. Here are some other snippets from the Vokera Compact installation & operational manual. I assume it's the same for the Vision Plus range. It's a lot to piece together:

screenshot 2.png

screenshot 3.png

screenshot 4.png

screenshot.png
 
John,

With the Vokera Vision , I think the 75% max for the first 15mins is linked to the type of primary heat exchanger that they use. It is (or appears to be) machined and welded from two blocks of an aluminium alloy. The control system maintains quite a tight limit on the differential temp between flow and return ( 15 degrees I think) - once exceeded it trips requiring a manual reset. My guess is that is all part of the control to limit that differential - on HW it is not an issue because of the high flow rate and quick return from the secondary.

The condensate also produces a white milky water with white grains - which if not flushed annually - eventually blocks the discharge line ahead of the trap. I am told this initially stems from the fluxes used in the manufacturing process - but is a sign of other issues if it continues after the first couple of years.

Having said that - other than that one nightmare, all the others I have dealt with have been fine - but then when you have stripped and rebuilt one a few times, you become a pocket expert.
 
Interesting because I also discovered that whoever installed the relations 20S installed the magnetic filter adjacent to the HW cylinder and its installed as a full fledged bypass ie its connected across the flow and return (presumably by mistake) so no problem with excessive delta T there!!, strangely enough even though the system is regularly run with only 2 rads (zoning, in a small house) with a combined output of ~ 2.5 kw causing the boiler to cycle regularly, it never causes any problems, just a 3 minute anti rapid cycling time and as stated previously only exceeds the SP by 2C for a few minutes before going on to cut out at SP+5C maybe 5 minutes or so later. Whatever about boiler efficiency due to the higher return temperature there may in fact not be a huge difference in the delta T (vs with filter installed properly) due to the much higher circulating flow but the overall temperature rise in very rapid which one might think wouldn't be great for the Hx.
 
John,

With the Vokera Vision , I think the 75% max for the first 15mins is linked to the type of primary heat exchanger that they use. It is (or appears to be) machined and welded from two blocks of an aluminium alloy. The control system maintains quite a tight limit on the differential temp between flow and return ( 15 degrees I think) - once exceeded it trips requiring a manual reset. My guess is that is all part of the control to limit that differential - on HW it is not an issue because of the high flow rate and quick return from the secondary.

The condensate also produces a white milky water with white grains - which if not flushed annually - eventually blocks the discharge line ahead of the trap. I am told this initially stems from the fluxes used in the manufacturing process - but is a sign of other issues if it continues after the first couple of years.

Having said that - other than that one nightmare, all the others I have dealt with have been fine - but then when you have stripped and rebuilt one a few times, you become a pocket expert.

Many thanks for this info.

I have purchased a Wiser smart thermostat and WiFi TRV's. I think it's the case, that if the Wiser Hub is just connected as a standard on/off connection to the boiler, then all the boiler modulation and control specifics you have outlined above will still be retained?

The Vision Plus has OpenTherm, as does Wiser; but when I spoke with Vokera, they said that most 3rd party smart systems with OpenTherm are not compatible with the Vokera OpenTherm. Well so much for the "open" communication protocol! But again, would OpenTherm instructions override the boiler modulation and other Internal controls?
 
My experience with Opentherm with Vokera is not very positive. I have tried on three separate systems to integrate the former Honeywell Evohome system with Vokera products. The results have been unpredictable and in one system led to lockouts on overheat.

I am sure that these issues are resolvable - but it is not plug and play - which is what I need to sell systems that are seamless in their compatibility.

Others probably have had better experiences
 
My experience with Opentherm with Vokera is not very positive. I have tried on three separate systems to integrate the former Honeywell Evohome system with Vokera products. The results have been unpredictable and in one system led to lockouts on overheat.

I am sure that these issues are resolvable - but it is not plug and play - which is what I need to sell systems that are seamless in their compatibility.

Others probably have had better experiences

Thank you for this info. I think I will just leave it un-connected. With the modulation and other control aspects of the boiler, together with the Wiser system, I think I will be 95% of the way there.
 
eg: You come back from holiday in mid-Jan, and it's minus 5C outside. The heating has been off for 3 weeks, and everything is stone cold. So you want to heat the CH water as quickly as possible, and the radiators are shedding large amounts of heat, as the rooms are so cold.
You are forgetting that a heating system is sized for exactly those conditions (though usually -3C outside). It doesn't assume that the internal temperature has only dropped (e.g) five degrees. If the heat loss calculation says you need a 15kW boiler, you need a 15kW boiler;.fitting a 30kW will not achieve anything. But if you have a combi which produces 30kW for heating, then range rating down to near 15kW would be a sensible thing to do.
 
We shouldn't forget that if the system is down overnight then the boiler must reheat say 75/100 litres of water from say 20C to say 70C which requires ~ 4.4 kwh minimum, as this is being heated up, the rads will start emitting heat as well but it does take extra time to achieve full operating temperature, my ~ 15 kw heating load with 85 litre of water heated by a 20kw oil fired boiler takes 25 to 35 minutes in the morning before reaching 70C and cut out.
 
You are forgetting that a heating system is sized for exactly those conditions (though usually -3C outside). It doesn't assume that the internal temperature has only dropped (e.g) five degrees. If the heat loss calculation says you need a 15kW boiler, you need a 15kW boiler;.fitting a 30kW will not achieve anything. But if you have a combi which produces 30kW for heating, then range rating down to near 15kW would be a sensible thing to do.

This is such an interesting conversation, and much appreciated.

From my (limited) understanding, my property's heat loss, is calculated at an external temp of -3C and in internal temp of 20C. Let's say for example the total is 13kW. My boiler will need to run, on average, at 13kW to maintain this constant internal temp of 20C, assuming all other factors, including the external temp of -3C remain constant.

But if we now consider the conditions I outlined above namely: -5C outside and -5 inside — due to leaving the house empty and unheated during a 2 week cold-spell. With this scenario, when I return from holiday, I now wish to heat the house as quickly as possible to reach 20C, and so the boiler can ramp-up to 30kW, and then modulate down to 13kW when 20C is reached?

In practice, the boiler would only increase its output so the flow temp maxes to say 80C; and the radiators would be able to shed far more heat, as the delta is now D78 and not D50 (or even lower). (Av rad temp of say 75C, and an internal temp of say -3, gives a delta of D78).

Any thoughts? Is this a correct analysis?

Hence why, it seems, that when you have a modulating boiler, you don't need to range-rate it, and indeed if you did so, it would not make the boiler as useful and as quick to rapidly heat the house when you needed to.

Of course, I understand that in practice, you would be better to perhaps leave the heating on at a low-level whilst you are away for a number of reasons.

Thanks!
 
Last edited:
If you de rate the boiler to match the heating load, say 13kw above and you come home to a freezing house, and because you want a reasonable quick heat up in some rooms initially, then simply just heat the ground floor for a hour or two, you will then get a very rapid heat up to operating temperature and then the boiler will modulate to maintain this heat load of ~ 50%, then switch in your second zone and this will heat up, at a slower rate admittedly but you won't suffer any great discomfort IMO. In practice, I don't think anyone really sets the boiler output to exactly match the heating load. If it was my house and I had a 30kw boiler with a 13kw heating load I would de rate to maybe 18 to 20kw.
Also the de aerating isn't written in stone and is settable and I think in some cases the user can select his heating output from a menu?.
 
But if we now consider the conditions I outlined above namely: -5C outside and -5 inside — due to leaving the house empty and unheated during a 2 week cold-spell. With this scenario, when I return from holiday, I now wish to heat the house as quickly as possible to reach 20C, and so the boiler can ramp-up to 30kW, and then modulate down to 13kW when 20C is reached?
Assuming the system stills works at all and hasn't been destroyed by freezing, it would depend on the design of the radiator system, i.e. size of radiators and how they are piped. A system designed to emit 15kW max (at say 60°C flow) is going to struggle to emit more than about 23kW max (at say 80°C flow)

The 'perceived temperature' of a house depends roughly 50:50 on the air temperature and the temperature of the surfaces. You can get the air temperature up fairly quickly (hours) but warming the fabric of the building can take several days.

I'd recommend that you leave the house with the heating set at 10°C and the stopcocks off.
 