Could someone work out total KW input for the following applying the diversity factor.
36 KW combi
24 KW combi
Cooker 12.9kw
It would appear according to gas Safe that my original assessment was wrong that they had exceeded badge capacity of a U6 as I didn't apply diversity factor.
Now the original plumber recorded 10mb working pressure with both boilers working on hw. My take is that you use the highest rated appliance not both. I also noted that all three appliances exceeded badge capacity. Now after working out diversity it comes in at 55.74kw.....is my calculation correct