My existing system boiler if fed via a fused connection unit off the ring final circuit, when the boiler is replaced is it a requirement/best practice, that the boiler is fed via a dedicated circuit from the consumer unit to the fused connection unit.
Cheers
Ian
Leaving it on the ring circuit is not "Best Practice". A dedictated circuit is.
Hi,Contributing as spark ... no
Why do you ask
Hi,
If a new circuit is required I can get this sorted in advance of the boiler replacement.
Leaving it on the ring circuit is not "Best Practice". A dedictated circuit is.
Thanks to the forum I now know is not an 'electrical' requirement, is the dedicated circuit preferred by plumbing professional trade bodies as best practice
If you are having an electric boiler fitted, yes a dedicated circuit would be required ...but for a gas boiler absolutely not a requirement.
I may be wrong but an elec boiler rated at 3kw should be fine ?
Hum.... I wouldn't, sure if it had a 13A plug on it but anything with a load above 2 Kw should be on its own circuit
Surely that depends on what it is supplying.Rubbish.
Surely that depends on what it is supplying.
Surely that depends on what it is supplying.
No. I edited my own response. Touch of paranoia?I note you have edited my full response
Are you a troll
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.like????
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.
A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.
There are no regulations that state this ..
But there are regulations about spurs off spurs, which plumbers tend to ignore.
You are missing the point as this is not about regulations, but what is correct for a particular scenario. You are generalising for a boiler.
Equally electricans often fail to understand controls.There are no regulations that state this ..
But there are regulations about spurs off spurs, which plumbers tend to ignore.
He asked about Best Practice, not just the minimum requirement under the Regs. Surely that can differ?Err no.
I am offering a direct answer to the op.
His question was do I need a dedicated fused spur for a new gas boiler.
The answer is no.
Murdock - You surely understand what I am saying her and if you where so up on your Regs you would not disagree with this. Have we touched a nerve?A dedicated supply to a piece of equipment you do not want disturbed by tripping from faults by other electrical items or that requires more sensitive RCD’s or different protection to that provided in a standard CU.
What makes you think you are the only electrician on here?
3kW wouldn't keep the house very warmI may be wrong but an elec boiler rated at 3kw should be fine ?
3kW wouldn't keep the house very warm
I don't, but I'd hazard a guess that if it's for a whole house the heat requirement is well above 3kWHow do you know the heatloss
I appreciate your logic and your quite right I would guess a whole house is above 3Kw. A jobwe did recently did surprise myself I had to double check my calcs.I don't, but I'd hazard a guess that if it's for a whole house the heat requirement is well above 3kW
Not touched a nerve . Just making sure an unsuspecting client isn't badly advised by a plumber, regarding electrical regulations.
It's that simple.
Thanks to the forum I now know is not an 'electrical' requirement, is the dedicated circuit preferred by plumbing professional trade bodies as best practice
BS7671 314.1 Every installation shall be divided into circuits, as necessary, to:Vee- you can disagree with me you like, but please offer up a BS 7671 reg number to back up your position
Are there systems out there with usual pump and rads, but electric boiler? I've never seen one, not that that proves anything. I'd have thought if you were going for electric you might as well have a heater in each room, or even storage heaters.I appreciate your logic and your quite right I would guess a whole house is above 3Kw. A jobwe did recently did surprise myself I had to double check my calcs.
A barn conversion with heat pump in mind from the beginning. The total heat loss for 3 bed, 2 en-suite, lounge dinner, large kitchen etc. etc. was just 4.2 Kw. It cost a few quid and there was plenty of non standard work but shows things can be done very well when the money is there. Sorry to hijack the post
BS7671 314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid danger and minimise inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance.
& (iv) reduce the possibility of unwanted tripping of RCD's due to excessive protective conductor (PE) currents not due to a fault
BS7671 314.2 Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
Interpretation of Best Practice within this is of course in the eye of the electrician.
Are there systems out there with usual pump and rads, but electric boiler? I've never seen one, not that that proves anything. I'd have thought if you were going for electric you might as well have a heater in each room, or even storage heaters.
And your point is?
The above points are relevant to new designs and considerations for changes to existing installations.
Swapping a boiler is neither of the above
You are precisely the type of individual that goes out of their way to confuse un-suspecting clients and spend unnecessary money.
A gas boiler does not need to be on a individual circuit..
For all you know the OP may have any older fuseboard with a single upfront RCD .. so putting in another circuit would have absolutely no benefit to him.
And new circuits fall under Part P of the building regs too.
Yes, but surely the minute you touch an existing installation, you start to become responsible for it?
If I have BS 3036 fuses and rubber cable in poor condition and then I replace my electric cooker with one of similar current draw to the existing one, I would not be changing an existing installation either, but can I legally do so? I know you can't do it the other way around (i.e. put a new circuit in to feed a piece of electrical equipment that is only running on Grandfathers' rights, and also in poor state), but can you do it this way round? My feeling is that, like running a new light fitting onto a circuit that would not pass an EICR, the answer is 'no'.
Having said all that, I would agree that most electricians would probably not interpret the regulations to mean a new boiler MUST be on an independent circuit, as Vee has not denied.
You conviently ignore the OP's question/reference of "Best Practice". I accept and did not contradict your minimum standard you wish to apply is legally acceptable. That does not make it the best way of dealing with it. Surely anyone is allowed to promote a better way of doing things in order to give customers a choice. Especially when they are informed,willing and wanting to pay for that.Not if all you are doing is disconnecting 1 accessory and connecting a new one.
The OP's question was does a new gas boiler (in an existing installation) need to be on a dedicated circuit.
The answer is no.
What an designer / installer would do on a refurb/ rewire / new build is a completely different question all together
You conviently ignore the OP's question/reference of "Best Practice". I accept and did not contradict your minimum standard you wish to apply is legally acceptable. That does not make it the best way of dealing with it. Surely anyone is allowed to promote a better way of doing things in order to give customers a choice. Especially when they are informed,willing and wanting to pay for that.
You conviently ignore the OP's question/reference of "Best Practice". I accept and did not contradict your minimum standard you wish to apply is legally acceptable. That does not make it the best way of dealing with it. Surely anyone is allowed to promote a better way of doing things in order to give customers a choice. Especially when they are informed,willing and wanting to pay for that.
I've covered this in my responses .... If the OP is happy to have boards lifted, walls chased, floors disturbed then its UP TO HIM
But there is absolutely NO NEED in existing installations.
Do you insist on zoning houses when you change a boiler?
Zoning is a building reg mate so it's needed
When you just change a boiler?
So what your point?I've covered this in my responses .... If the OP is happy to have boards lifted, walls chased, floors disturbed then its UP TO HIM
But there is absolutely NO NEED in existing installations.
Do you insist on zoning houses when you change a boiler?
Got smacked . so when our boiler needs replacing our house has to be zoned ?
Most new boilers I see are simple like for like changes ...
One refurb I’m on, a flat isn’t zoned ...neither was the last house refurb I was on .. what are the GSR s upto then ?
Most new installs in refurbs are zoned . but not all ..