Messages
185
I am looking to install a thermal store to replace my current vented cylinder. I plan to use an external plate exchanger for DHW and heat the store directly from my existing vented boiler. So what I am looking for is a plain stainless steel tank (no internal coils) with a variety of connections. It would need to have at least 2x22mm (or bigger) towards the top, at least 2x22mm at the bottom, a place for a cylinder stat, and a connection for a backup immersion heater.

So far I have found the Gledhill Flexible Buffer store (PLU300MB) that looks like could work, although it would be nice if it had 2 stat pockets and the upper connections were spread out (vertically) a bit, like in their regular buffer store PLUDR300B. Unfortunately the PLUDR300B does not have a spot for an immersion heater.

Any one know of anything similar from other manufacturers?
 
I am looking to install a thermal store to replace my current vented cylinder. I plan to use an external plate exchanger for DHW and heat the store directly from my existing vented boiler. So what I am looking for is a plain stainless steel tank (no internal coils) with a variety of connections. It would need to have at least 2x22mm (or bigger) towards the top, at least 2x22mm at the bottom, a place for a cylinder stat, and a connection for a backup immersion heater.

So far I have found the Gledhill Flexible Buffer store (PLU300MB) that looks like could work, although it would be nice if it had 2 stat pockets and the upper connections were spread out (vertically) a bit, like in their regular buffer store PLUDR300B. Unfortunately the PLUDR300B does not have a spot for an immersion heater.

Any one know of anything similar from other manufacturers?
Why the thermal store and not an Unvented cylinder? Have you got external heat sources like Wood burners etc.
 
Why the thermal store and not an Unvented cylinder? Have you got external heat sources like Wood burners etc.

In addition to mains pressure hot water, I would like to have heat flowing to the radiators whether the boiler is running or not. My heating loop will use a modulating pump (Grunfos alpha 2) and TRVs all round.
 
I am looking to install a thermal store to replace my current vented cylinder. I plan to use an external plate exchanger for DHW and heat the store directly from my existing vented boiler. So what I am looking for is a plain stainless steel tank (no internal coils) with a variety of connections. It would need to have at least 2x22mm (or bigger) towards the top, at least 2x22mm at the bottom, a place for a cylinder stat, and a connection for a backup immersion heater.

So far I have found the Gledhill Flexible Buffer store (PLU300MB) that looks like could work, although it would be nice if it had 2 stat pockets and the upper connections were spread out (vertically) a bit, like in their regular buffer store PLUDR300B. Unfortunately the PLUDR300B does not have a spot for an immersion heater.

Any one know of anything similar from other manufacturers?
Gledhill ...Uck there has never been anything decent come out of that Blackpool outfit
centralheatking
 
Gledhill ...Uck there has never been anything decent come out of that Blackpool outfit
centralheatking

Yes, I have read a lot of complaints about them, which is why I am looking for other makes.
 
Why not use a twin coil unvented in reverse

eg gledhill 400l sol

use the twin coils for hot water etc?
 
Why not use a twin coil unvented in reverse

eg gledhill 400l sol

use the twin coils for hot water etc?

Typically the coils are too small (1-2 m^2 surface area), even in most commercial thermal stores, which is why people think stores need to run at 80C to work. I plan on running mine at 60C. I also live in Norwich, which has very hard water and I am worried a bit about internal coils scaling as well.

Something like this would work, the 300l version has a 4.1^2 area coil:
Hygienic Buffer Storage Tank Vertical - http://plumbingsupplies24.co.uk/hygienic-buffer-storage-tank-vertical/

But it is a mild steel tank, so it would need to be a sealed system. In the UK people are a bit fearful of sealed hot water systems, so there are a lot of hoops to jump through for a DIY install.
 
Typically the coils are too small (1-2 m^2 surface area), even in most commercial thermal stores, which is why people think stores need to run at 80C to work. I plan on running mine at 60C. I also live in Norwich, which has very hard water and I am worried a bit about internal coils scaling as well.

Something like this would work, the 300l version has a 4.1^2 area coil:
Hygienic Buffer Storage Tank Vertical - http://plumbingsupplies24.co.uk/hygienic-buffer-storage-tank-vertical/

But it is a mild steel tank, so it would need to be a sealed system. In the UK people are a bit fearful of sealed hot water systems, so there are a lot of hoops to jump through for a DIY install.

each coil is 20 kw so if you combine them that should give you a hot water of around 20kw (to be safe)

why not just buy a thermal store? as there designed for what your planning?
 
each coil is 20 kw so if you combine them that should give you a hot water of around 20kw (to be safe)

why not just buy a thermal store? as there designed for what your planning?

Aside from being overpriced, most commercial thermal stores are not designed to deliver 12lpm of hot water while running at 60C. The DHW coils are too small. There are a few exception like the steel OEG store I linked above, I lived with that one for a few years in my previous house and it worked great. It has a 4.1sq.m corrugated stainless coil, so I that would be around 150kW given an average differential of 30C and an estimate of 1.2 kW/m2/k for the coil. To get 12lpm of hot water from 5C to 40C you need 30kW. The problem is that exchangers are typically rated for a 40C differential, which is not realistic for a 60C tank. Drop that to around 12C differential and you need 100kw. A 100kW plate exchanger is pretty cheap, and serviceable.
 
if you suffer from hard water plate hex is out of the question as it will get blocked very easily and once it blocked you will need to replace it

have a word with these people


gledhill make a 3.7m2 coil on there thermal stores also they do one with an external plate
 
Last edited:

Reply to Cylinder for DIY thermal store in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I am in process of replacing an existing sink with a new stainless steel one. The existing tap is plumbed directly to copper which means that it...
Replies
6
Views
322
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
455
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
220
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
319
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...