Sooo...

Let's say you go do a gas safety and the boiler has the following readings on the analyser:

Co: 346
Co2: 10.8
Ratio: 0.0032

Would you

A) AR it
B) pass it and recommend a service
C) pass it with no recommendations
D) ID it
 
like he said..what is ppm .lol

surley, it depends on boiler and class!

some state co reading only, ideals different to baxi or is it open flue?????
the ratio is bordering though so i would be looking at the flue with that co2 reading or heat shields/path!
if its cast then sooted up?

then again i am just guessing on a conundrum and go with A because its getting there.lol
 
Without looking in my book I'd guess at C but as it is so close to being over the co limit and ratio I would still recommend a service.
 
It was a vaillant ecotec pro 24.. My book says max ratio is 0.008 so technically the boiler is well within the safe limits.. So I passed it with a recommendation for a service to bring the co level down.. Just wondered what you guys would have done ... On another not I just changed my email address and now I'm not getting notifications of replies to my threads :/
 
Screenshot_2016-03-21-20-34-35.jpg

Every reading is too high. It may need gas valve adjustment but I also think it needs a clean or recirculation of poc is happening.
 
Last edited:
I had a Baxi with very high co.....turned out to be a flue seal, but the custard was on holiday so just turned it off until it was replaced.
 
Bloody hell, you gas lot get away with murder. I'm not happy on the oil unless the co is under 20 ppm.

anything over 100 and theres something wrong with condensing boilers
 
Unless stated in MI's it's 0.008, anything over 0.004 then full service recommended but if it's under 0.008 and MI's don't mention FGA ( so basically all the old ****e ) then you can pass safe if all other checks are as they should be
 
Its always been 0.004
0.008 is only allowed after a service to allow for all shiite flying about. Although never had one go up after a service

I spoke to gas safe to clarify this and they said its 0.008 and always has been. It's only 0.004 when MI states which is basically all high efficiency boilers. If MIs don't mention FGA at all then you don't have to do it, as long as other checks fall in line
 