I have read on him yes. Im just running numbers and trying to figure out the resulting flow from the square root of head. Clearly im not doing something right
You mean mathematically?. if a differential head of 3M results in a flow of say 13 LPM (like my heating system) and I increase the (pump) head to say 5M, the resultant flow will be the original Flow X the sqroot of the (newhead/oldhead).....13X sqroot(5/3) = 13X1.29 = 16.77 LPM.
 
You mean mathematically?. if a differential head of 3M results in a flow of say 13 LPM (like my heating system) and I increase the (pump) head to say 5M, the resultant flow will be the original Flow X the sqroot of the (newhead/oldhead)***..13X sqroot(5/3) = 13X1.29 = 16.77 LPM.

Thanks buddy. That makes sense now
 
You mean mathematically?. if a differential head of 3M results in a flow of say 13 LPM (like my heating system) and I increase the (pump) head to say 5M, the resultant flow will be the original Flow X the sqroot of the (newhead/oldhead)***..13X sqroot(5/3) = 13X1.29 = 16.77 LPM.
Although they both have this part number DAB 60161174, the images look different......the Amazon one is more expensive Andries than even look like it has the data display.....
Will phone PSD tomorrow and confirm, think this is my best hope, seems a very good price £62.39 inc free postage....any thoughts ? 1st image PSD 2nd image Amazon
 

Attachments

  • BAD5AB6E-2778-4689-9750-3CB4E74C7278.jpeg
    BAD5AB6E-2778-4689-9750-3CB4E74C7278.jpeg
    30.7 KB · Views: 11
  • 26BC1EB3-4F14-48D9-ADBE-780AC403D24A.jpeg
    26BC1EB3-4F14-48D9-ADBE-780AC403D24A.jpeg
    89.1 KB · Views: 8
Every time one looks at these pumps they seem to change spec/display, Grundfos is the same, they must be breeding them, just ensure you are getting the one with the proper display.
 
A bit surprised at that, don,t know dimensions of your own one, the wilo gives practically the same output, will check in morning to compare and advise, measure your own to confirm 130mm
 
A bit surprised at that, don,t know dimensions of your own one, the wilo gives practically the same output, will check in morning to compare and advise, measure your own to confirm 130mm
The DAB3 appears to be a 8M pump hence the 180mm between centers so I would advise against this as it involves piping mods and drain down, also 130mm centers gives you more choice of 6/7M pumps.

While the Wilo or Dab Evosta2 (no display) will almost certainly give you the required head/flow I think you are better off installing a pump like a Grundfos UPS3 15-50/65 which is very powerful 6.5M pump which will satisfy your needs with ease. For example it will pump 33LPM @ 4.5M, Dab2, 33LPM @ 3M and the Wilo 33LPM @ 3.2m.

Unfortunately, this UPS3 does not display watts but not the end of the world as you really only need this as an aid to see if you have a pump problem or a restriction. By spending a few extra bob you can buy a nice little plug in energy monitor, I have a few and they are quite accurate, (see link) and use it like this.

I assume you intend to clean the existing pump head so before removal/clean, remove the pump lead and fit a 3 pin plug. ensure boiler off and any zone valves if fitted, latched open, plug in the pump lead to the energy monitor in turn plugged in to any convenient socket or extension lead, note the watts, remove plug, clean pump head and ports, then re measure power.
Depending on findings, if you do decide to install the UPS3 or whatever, do likewise, stick a 3 pin plug on it and you can then monitor its power in its different operating modes and then run the pump on the appropriate setting. When tests complete re install pump lead to wiring center.

One word of caution if removing the pump by opening the isol valve nuts, these can be extremely difficult to undo, I have change out a few pumps for neighbors and one of my own and have always drained down and removed the pump complete with isol valves, I then found it quite difficult to remove the pump valves even though I obviously renewed them with the new pump.


PS: fairly sure your pump has 130mm centers but best to measure up.
 
Last edited:
Thanks for all the advice, sounds like the way to go.....will investigate the power to my pump, looks rather complicated, as this also had its wiring modified.....when an electrician came round a few years ago, he made some changes, involved lifting up the floor board to get access o the connections ( my dam extension buile
der 🤯 ) found he had used a light switch as a junction box, now the new junction box in the immersion cupboard, but looks complex.....will have a careful look, taking photos as I go....all good fun 😂 what’s the LPM of the DAB3 ? Do like the idea of the displays, womder how it displays the flow, ant be a calculation as it doesn’t know the Delta T, must be an integral flow meter 🤔

I don’t suppose a replacement pump comes with new valves, assume would have to be bought separately 🤔 my CH pump iso valves have no handles, never have, can these be bought separately ? Be so much easier to isolate
 
Your old pump isolating valves are probably 1/4 turn ball valves that you shut with a screwdriver (slot) or a allen key, nothing sticks out, but unfortunately they almost always leak after operation, you can easily buy new ones with gate valves.

It would seem that you can get a Dab Evosta3 with 130mm centres. it might be a 6.5/7M pump but you should ask your supplier if they have one, this will also be adequate IMO, the pump curves for all their models are in the link.

 
Your old pump isolating valves are probably 1/4 turn ball valves that you shut with a screwdriver (slot) or a allen key, nothing sticks out, but unfortunately they almost always leak after operation, you can easily buy new ones with gate valves.

It would seem that you can get a Dab Evosta3 with 130mm centres. it might be a 6.5/7M pump but you should ask your supplier if they have one, this will also be adequate IMO, the pump curves for all their models are in the link.

have ordered the DAB 3 21412 model, not sure which curve is applicable to the pump I ordered.... some websites don’t give the numbering, just the performance data, the site I bought mine from had some contradictory info, confirmed it was 130mm and 6.9m head by phone and has a 5 year guarantee not 3 as shown, hopefully they will change the info on their site...ordered it from https://plumbingsuppliesdirect.co.uk/dab-evosta-replacement-grundfos-circulating-heating-pump/ but the invoice is from STUART PLUMBING & HEATING SUPPLIES, but on their website it’s more expensive and have to pay postage 🤯 so assume PSD is owned by Stuart plumbing.....must be offering competition to their own company.....marketing strategy 😎 the pump seems to have numerous control options, what’s my best setting to start with ? And best setting long term....

P.S. the pump iso valves are gate valves, not quarter turn, with a single square 1/4” approx post, no thread that I can see to hold a handle, can’t understand why they are sold like this, to shut off in an emergency, requires hunting around for an adjustable ( or normal ) spanner.....so much easier with a handle......maybe will replace them when I change the pump 🤔
 
Last edited:
have ordered the DAB 3 21412 model, not sure which curve is applicable to the pump I ordered.* some websites don’t give the numbering, just the performance data, the site I bought mine from had some contradictory info, confirmed it was 130mm and 6.9m head by phone and has a 5 year guarantee not 3 as shown, hopefully they will change the info on their site...ordered it from https://plumbingsuppliesdirect.co.uk/dab-evosta-replacement-grundfos-circulating-heating-pump/ but the invoice is from STUART PLUMBING & HEATING SUPPLIES, but on their website it’s more expensive and have to pay postage 🤯 so assume PSD is owned by Stuart plumbing.*.must be offering competition to their own company..marketing strategy 😎 the pump seems to have numerous control options, what’s my best setting to start with ? And best setting long term.

P.S. the pump iso valves are gate valves, not quarter turn, with a single square 1/4” approx post, no thread that I can see to hold a handle, can’t understand why they are sold like this, to shut off in an emergency, requires hunting around for an adjustable ( or normal ) spanner..so much easier with a handle...maybe will replace them when I change the pump 🤔
You have the correct type isol valves as the gland nut can be tightened up if any leak, so no need for renewal.

Would suggest constant pressure, either CP2 or CP3 see below, answer to SJB.
 
John what would happen to the watts display if there was a pump problem or restriction in the system?
Look at the pump curve on pge 25 in attachment which is for a 7M Evosta2, can,t find one for a 7M evosta3.
you will see that on constant pressure CP3 that the pump will maintain 4.8M from 0 flow, if the system demand is 1 m3/hr 16.7 lpm then the pump power is 35w, if a restriction in the system and the flow fell to zero then the power is 16.5w and so on in between. more later
 

Attachments

  • Evosta-2-3-Installation-and-Operation-Manual_UK.pdf
    3.4 MB · Views: 10
Last edited:
Thanks John. As I said the other day, the ins and outs of pumps is new to me, so still trying to figure the charts. I understand what you said above but feel free to share more in case I missed something 👍
 
Thanks John. As I said the other day, the ins and outs of pumps is new to me, so still trying to figure the charts. I understand what you said above but feel free to share more in case I missed something 👍
I am in the same boat as you, things are always so complicated until you understand them, then you wonder why it was so difficult......it’s not rocket science.....so we‘ll get there 🙏 keep asking questions, it’s the only way to learn.....also when people understand something so well it’s sometimes easy to downplay an answer.....I will persevere, I want to understand this.....trouble is the pump I ordered has lots of options so need to understand that also, just hope the others are patient with me 🤞
 
Thanks John. As I said the other day, the ins and outs of pumps is new to me, so still trying to figure the charts. I understand what you said above but feel free to share more in case I missed something 👍
Page 25 shows two graphs the top one is the normal pump curves and I am just assuming that you have choosen the pump to run on setting CP3 and just suppose that your system will circulate 16.67 LPM at this setting of 4.8m. if you look vertically downwards you will see another graph of power vs flow for all the different pump settings, you have choosen CP3 and because the system is circulating at 16.67 LPM then the pump power required is 35W, if the system, say boiler Hx starts getting dirty/fouled then the pump speed will reduce to maintain this constant head of 4.8M and if it got completely blocked the pump will still maintain 4.8m but with no flow and still require 16.5W. If you had a smaller system in that even when spotelessely clean only circulates 8.3 LPM (0.5m3/hr) then you can see that the pump only requires ~ 25.5W at the constant pressure of 4.5M.

If you take my system as a example which circulates ~ 15 LPM (0.9m3/hr) @ 3.5M.......I could set the pump to CP2 which is constant pressure at 3.8M, my system would then circulate 15.7 LPM (0.94 m3/hr) @ 3.8M.
with a power demand of 26W.

I woud suggest CP2 (3.8M)as a reasonable starting point, it can very quickly be changed especially with all the info that will be displayed on this pump.
 
Last edited:
I am in the same boat as you, things are always so complicated until you understand them, then you wonder why it was so difficult...it’s not rocket science..so we‘ll get there 🙏 keep asking questions, it’s the only way to learn..also when people understand something so well it’s sometimes easy to downplay an answer..I will persevere, I want to understand this.***.trouble is the pump I ordered has lots of options so need to understand that also, just hope the others are patient with me 🤞

My background is oil fired appliances, thats all we were, burner technicians. The system side of things is not something we did much of, so this last year I've been studying and learning a lot of new things to better my understanding. I have a passion for learning and a desire to at least have a good understanding in all areas of heating systems. John here has taught me a few things that I didn't know before joining this forum and to be honest, when it comes to pumps he's probably one of the best on here.
 
John what would happen to the watts display if there was a pump problem or restriction in the system?
Hi
i can only relate to my experience in the oil industry ( Mobil Coryton refinery ) when the pump discharge was shut back ( or there was another restriction to flow ) on a centrifugal pump the Amps ( power ) would drop off, as the pump would just be stirring the liquid and not doing any real work......not sure if that’s applicable, but IMO should be....
 
That would be pretty correct, all very large centrifugal pumps are started with the discharge valve shut to avoid the motor tripping on overload, the discharge vale is then opened gradually.
 
Page 25 shows two graphs the top one is the normal pump curves and I am just assuming that you have choosen the pump to run on setting CP3 and just suppose that your system will circulate 16.67 LPM at this setting of 4.8m. if you look vertically downwards you will see another graph of power vs flow for all the different pump settings, you have choosen CP3 and because the system is circulating at 16.67 LPM then the pump power required is 35W, if the system, say boiler Hx starts getting dirty/fouled then the pump speed will reduce to maintain this constant head of 4.8M and if it got completely blocked the pump will still maintain 4.8m but with no flow and still require 16.5W. If you had a smaller system in that even when spotelessely clean only circulates 8.3 LPM (0.5m3/hr) then you can see that the pump only requires ~ 25.5W at the constant pressure of 4.5M.

If you take my system as a example which circulates ~ 15 LPM (0.9m3/hr) @ 3.5M.***...I could set the pump to CP2 which is constant pressure at 3.8M, my system would then circulate 15.7 LPM (0.94 m3/hr) @ 3.8M.
with a power demand of 26W.

I woud suggest CP2 (3.8M)as a reasonable starting point, it can very quickly be changed especially with all the info that will be displayed on this pump.

Thanks again John. I've checked everything against the charts and did the maths for your bottom paragraph and it all adds up. Thanks for taking the time 👍
 
I'll go through another two settings, constant curve (CC) and the most interesting one of all, proportional pressure (PP) control, based on my own system, tomorrow.
 
Ok, at tremendous expense here are a few numbers/attachments based on my requirements of 15 LPM @ 3.5M head and also based on the TRVs closing down with flow demand as low as 5 LPM.

speed2 will give 16 LPM@4M and 29.5W
speed2 will give 5 [email protected] and 27.5W

CP2 will give 15.9 [email protected] and 26W
CP2 will give 5 [email protected] and 17W

PP3 will give 16.8 [email protected] and 30W
PP3 will give 4.5 [email protected] and 12W

PP2 would almost do the job, [email protected] and (only) 12.2W.
 

Attachments

  • Evosta-2-3-Installation-and-Operation-Manual_UK.pdf
    3.4 MB · Views: 10
Don't seem to be able to attach other file above so attached it here, but can't.
Its zipped excel file so don't know why not.
 
Last edited:
CC or constant curve or fixed speed, the pump runs at a constant speed, the faster the speed the greater the head, all pumps have 3 CCs to cater for different size systems, the problem is the power consumption is almost constant because as the heating (flow) demand goes down due to zone vale closing or TRVs throttling in the pump head increases and the pump efficiency falls off as you can see by the tiny differences in the power consumptions between 15 LPM and 5 LPM.
CP or constant pressure is one of the best controls, the head stays constant due to the pump speed changing up/down to maintain the same head for different flowrates and gives big energy savings like above. 17W vs 26W.
PP or proportional pressure control can give the biggest savings of all as the pump (speed) and head decreases as the flow demand decreases, unfortunately because of the limited number of settings one sometimes has to select a higher setting than necessary like above, where PP2 falls just short of the required flowrate but only consumes 12W, the reason I choose the Wilo is that the PP settings can be incrementally changed in 0.1M stages to give any flowrate required.
Also PP control reduces the (speed) head as the flow decreases, and vica versa unlike the CC settings.
 
Thanks John for a clear explanation. One last stupid question. I take it long before the introduction of erp products and modulating pumps all circulating pumps were just CC?
 