Discuss Central heating not circulating after New Navien Combi fitted to Santon Premier system. in the Central Heating Forum area at PlumbersForums.net

Sounds like you need to separate the system. Also is the old boiler a non condenser @ShaunCorbs and the rads possibly ∆T 60?

Yep

Low loss header as condensing boilers don’t like older systems tbh I would fit a plate heat exchanger to save the new boiler as I doubt they cleaned the system
 
About 10 miles away :) but I booked up sorry
 
Yep

Low loss header

Then if the old boiler was running at ∆T 11°c the pump would of been capable of the higher flow rate and pressure required to overcome index circuit.
Sounds like this needs a low loss header and suitably sized secondary pump. The secondary side pipework will be ok in size but the new boiler internal pump isn't capable.
Alarming really as the installer really should have considered this 🤔
 
Then if the old boiler was running at ∆T 11°c the pump would of been capable of the higher flow rate and pressure required to overcome index circuit.
Sounds like this needs a low loss header and suitably sized secondary pump. The secondary side pipework will be ok in size but the new boiler internal pump isn't capable.
Alarming really as the installer really should have considered this 🤔

Makes you laugh tho they thought a 15-70 would do 2” pipework it’s the state of the industry atm either people don’t care or they don’t know chances are it was a 25-80 or 32-80

Was he even commercially qualified to work on the install
 
Then if the old boiler was running at ∆T 11°c the pump would of been capable of the higher flow rate and pressure required to overcome index circuit.
Sounds like this needs a low loss header and suitably sized secondary pump. The secondary side pipework will be ok in size but the new boiler internal pump isn't capable.
Alarming really as the installer really should have considered this 🤔
I agree. The boiler developed a leak from the heat exchanger seal 9 weeks in and charged 200 quid to do a 35
minute job under guarantee. Now they do not want to know.
 
I agree. The boiler developed a leak from the heat exchanger seal 9 weeks in and charged 200 quid to do a 35
minute job under guarantee. Now they do not want to know.

Didn’t they call the manufacturer out ?
 

Reply to Central heating not circulating after New Navien Combi fitted to Santon Premier system. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
503
losing pressure
L
T
Hi We urgently need to get our h/w cylinder replaced because it's leaking. Our current system is oil boiler feeding underfloor downstairs...
Replies
2
Views
406
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
446
M
Hi, we have a back combi heater. Whenever the heating comes on it seems to lose pressure within a few hours and I have to refill each morning...
Replies
1
Views
404
Hi, I drained the the central heating, to remove a radiator. After refilling it, the heating now won’t work. It’s a combi . I’m getting this symbol
Replies
2
Views
432

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock