boiler only works for 3 minutes

Discuss boiler only works for 3 minutes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

bluesky

Gas Engineer
Messages
132
a friends boiler- ideal excel, room sealed, system--- works for only 3 minutes then stopped, the boiler looks very old, the gas pressure is fine, what is most common fault for the boiler? shall i check the flame detection electrode first?

cheers in advance
 
well is it going to lock out?does it have detection? if so do a continuity test on the probe and lead
 
hi gasman, do you mean there should be continuity between probe and lead? how much should it be?

SimonG, i have not seen the boiler, will check it out tomorrow,

cheers chaps
 
just had a look, the fun is running but no ignition at all now, the pump is fine, the flame detection lead has continuity, checked thermistor on the water pipe, both about 0.3Ohm, took off the pilot burner and looks very clean, i am thinking the electrode is gone because i cannot see the sparking when is fun is running, shall i buy a new ignition electrode? how to check it is ok or not?

cheers
 
Worth checking the Air Pressure Switch, if fan works but doesn't operate the APS it won't go to ignition.
 